Towel Radiator valve question - noobish

Soldato
Joined
12 Feb 2004
Posts
7,266
Location
Manchester
I've been balancing our central heating system at home and our bedroom rads have trv and usual lock shield on them.

On our bathroom towel rad it seems to have a pair of lock Shields on them, so how do i set them to balance? Or leave both full open?

At the moment I've left them both half turn from being off position, rad gets hot nicely but is this the correct way to do it?


free upload image
 
Soldato
OP
Joined
12 Feb 2004
Posts
7,266
Location
Manchester
Trv full, lock shield closed, then Quarter of a turn open of the lock shield

Then trv set to temp desired

I assume I just do quarter / half turn of the towel rad valves
 
Associate
Joined
21 Apr 2010
Posts
1,335
Location
Preston
Trv full, lock shield closed, then Quarter of a turn open of the lock shield

Then trv set to temp desired

I assume I just do quarter / half turn of the towel rad valves

To balance them correctly you need a thermometer.
The inlet should be 12 deg higher than the outlet.
Rads nearest the boiler will only need the lockshield slightly open whereas rads further away will need more.
 
Associate
Joined
3 Aug 2003
Posts
2,028
Location
Plymouth, UK
Slight hijack as have never heard of this and now want to do it......have just read some instructions and need a wee bit of clarification.

When doing the balancing, the lockshield refered to is the outlet, correct? And do you set the inlet (TRVs mostly in my case apart from manual in living room and en-suite bathroom) to fully open?
 