Hi,
I'm hoping someone has some ideas of what could be the problem with the UFH in our newly tiled shower room.
The shower room is heated by a wet UFH system, the same as the rest of the house. It's with an ASHP so has low flow temps (around 45 °C currently). The problem is that the new tiles are not getting very warm even after hours of the new loop running. All the other loops on the same manifold are working fine as they have been for years. The bit of exposed pipe for the new loop (flow and return) for the shower room is getting hot as expected but the heat doesn't seem to be coming through to the tiles.
What is weird is that the new loop runs through another little corridor which was tiled at the same time as the shower room but with different tiles, and the these tiles do get warm. Also the shower tray in the shower room gets warm, just not the tiles!
The tiles are just normal porcelain floor tiles from topps tiles, approved for UFH.
Anyone got any ideas what could be the problem? The builders are back in tomorrow and I want to discuss with them what can be done.
Under the tiles and adhesive is 50-60 mm screed with the UFH loop in, below that is 25 mm PIR celotex, below that is sand, and then concrete.
It's a small room so it's not a long loop, around 14 m in length.
I'm hoping someone has some ideas of what could be the problem with the UFH in our newly tiled shower room.
The shower room is heated by a wet UFH system, the same as the rest of the house. It's with an ASHP so has low flow temps (around 45 °C currently). The problem is that the new tiles are not getting very warm even after hours of the new loop running. All the other loops on the same manifold are working fine as they have been for years. The bit of exposed pipe for the new loop (flow and return) for the shower room is getting hot as expected but the heat doesn't seem to be coming through to the tiles.
What is weird is that the new loop runs through another little corridor which was tiled at the same time as the shower room but with different tiles, and the these tiles do get warm. Also the shower tray in the shower room gets warm, just not the tiles!
The tiles are just normal porcelain floor tiles from topps tiles, approved for UFH.
Anyone got any ideas what could be the problem? The builders are back in tomorrow and I want to discuss with them what can be done.
Under the tiles and adhesive is 50-60 mm screed with the UFH loop in, below that is 25 mm PIR celotex, below that is sand, and then concrete.
It's a small room so it's not a long loop, around 14 m in length.