I changed the weather curve overnight to 42C at -6 and 28C at 15. It always runs a couple of degrees warmer than the curve, so this gave a leaving water temperature of 31-33C when it was 11-13C outside through the night. It ran very nicely indeed, doing a 12 hour run where it used a steady 350-400w of power, consuming about 4.8kWh in total. COP was about 4.8.
The house is a nice 21C throughout, despite a very strong wind all night. I need another cold night like the night before to test it properly though, as last night was mild. It should tick along at 37-38C LWT, instead of the 40-42C of yesterday morning, which it didn't like. I suspect with the Daikin, it's happy until the LWT is too high for the heat loss of the house, so it can't shed the heat quick enough, return water temp rises too high and it keeps cutting in and out. As soon as I ran an offset yesterday of -4C, leaving water dropped to 38C and power use dropped from an average of 1.8kW to 900w, for a mere 3C drop in LWT.