Evening all. Having a mare with some multiway switching for lights in a flat I am decorating. I've just troubleshooted and fixed one of the rooms. It has 3 core red/white/blue cabling to two switches which were wire nutted in the pendant. Eventually figured out the original 3 way switching with supply at the pendant had been messed up and reinstated it, works as expected.
I've now got a 2 switch 1 pendant arrangement in the stairway which is not working.
Switch 1
Downstairs light switch
1 x 3 Core red/white/blue
Switch 2
Upstairs light switch
1 x 3 Core red/white/blue
1 x twin and earth red/black/bare
Pendant
1 x twin and earth red/black/bare
As a note there is no earth wired into the lighting circuit (I know, but I'm not running new cabling to facilitate this) This has made taking multimeter measurements difficult. However, I've measured some voltages between the bare disconnected cables and they are as follows:
Switch 1
Red - Blue = 156v
Red - White = 150v
Blue - White 9v (Phantom?)
Switch 2
Red - Blue = 72v
Red - White = 11v (Phantom?)
Blue - White 85v
Black - Red = 0v (twin and earth back/red/bare)
I've done some continuity testing and found the following continuity:
Switch 1 White - Switch 2 White
Switch 1 Red - Switch 2 Blue
Switch 1 Blue - Switch 2 Red
This baffled me a little as I SUSPECTED initially there was a two way switching arrangement with power in the pendant. Clearly there is no power supply in the pendant owing to the single twin and earth present. I'm struggling to identify which switch is housing the supply. I am also struggling to ascertain what king of cabling arrangement this is, some kind of 3-way as per the fixed bedroom? I am also a little baffled why the red and blues in Switches 1 & 2 have swapped continuity, as if they are two separate runs of 3 core with red and blue swapped in wire nuts/bonds elsewhere behind the wall.
Image of what cables I have presented where at this time:
Anyone got any ideas where to start?
I've now got a 2 switch 1 pendant arrangement in the stairway which is not working.
Switch 1
Downstairs light switch
1 x 3 Core red/white/blue
Switch 2
Upstairs light switch
1 x 3 Core red/white/blue
1 x twin and earth red/black/bare
Pendant
1 x twin and earth red/black/bare
As a note there is no earth wired into the lighting circuit (I know, but I'm not running new cabling to facilitate this) This has made taking multimeter measurements difficult. However, I've measured some voltages between the bare disconnected cables and they are as follows:
Switch 1
Red - Blue = 156v
Red - White = 150v
Blue - White 9v (Phantom?)
Switch 2
Red - Blue = 72v
Red - White = 11v (Phantom?)
Blue - White 85v
Black - Red = 0v (twin and earth back/red/bare)
I've done some continuity testing and found the following continuity:
Switch 1 White - Switch 2 White
Switch 1 Red - Switch 2 Blue
Switch 1 Blue - Switch 2 Red
This baffled me a little as I SUSPECTED initially there was a two way switching arrangement with power in the pendant. Clearly there is no power supply in the pendant owing to the single twin and earth present. I'm struggling to identify which switch is housing the supply. I am also struggling to ascertain what king of cabling arrangement this is, some kind of 3-way as per the fixed bedroom? I am also a little baffled why the red and blues in Switches 1 & 2 have swapped continuity, as if they are two separate runs of 3 core with red and blue swapped in wire nuts/bonds elsewhere behind the wall.
Image of what cables I have presented where at this time:

Anyone got any ideas where to start?