Any sparkeys, need some help

I'm having a custom made desk and to match it going with an industrial look and feel on the multi power output

I've ordered these 10 MK METALCLAD 13 AMP SINGLE SWITCHED PLUG SOCKETS http://www.ebay.co.uk/itm/321007711851?ssPageName=STRK:MEWNX:IT&_trksid=p3984.m1497.l2649

I want to join them togther, idealy using some metal tubing. Is there a fitting to go between thats precut perhaps? 25/30mm in length?

Also what wiring is best to use here?

Cheers
 
I do not know of anywhere that provides pre cut Conduit. The only alternative (provided you want it all to be in steel) would be to buy 9x 20mm Couplings and 18x 20mm Male Brass Bush.

This way, you could join up all the Sockets together. Where are you powering these up from?
 
they're designed for conduit.
They can be joined to gether with 20mm or 25mm pipe work which usually comes in 1 meter lengths.
They can be joined together with out conduit by using male and female couplers (glands).
You can knock the inserts out of the boxes to connect the conduit anyway you like.

My advice is to hirer a conduit bender and die from a tool hire shop makes bending and fitting so much easier. Also get a fish wire to help pull the cable through. Also try and get a coupler tool to tighten up the lock nuts and glands as its a royal pain the arse trying to get an adjustable in.
 
Ok. Is this going to be an independent wiring rig and just put onto a plug top (which I do not recommend at all) or wired on it's own individual circuit back to the mains?
 
To wire this I would suggest using 2.5mm singles cable. You could use Twin and Earth 2.5mm2 on a 20A Radial. Is this basically going to power IT equipment?

Would be much less hassle to simply treat it like a custom extension lead and wire it too a 13A Plug with 2.5mm flex.
Provided the desks socket load doesn't exceed 3kW it will be fine.
 
Before you choose what cable to wire all the sockets together you might want to tell us how you will be supplying power to the 10 metalclad sockets?

Are you going to have a plug (so you will plug it into a wall socket) with some cable running to the first socket, if this is the case then you will need 1.5mm 3 core flex (which has a maximum current carrying capacity of around 18.5 amps (15 amps when enclosed in conduit) but will be protected by a 13 amp fuse in the plug). If you do use flexible cable then you will also need a compression gland on the first metalclad socket, this, when tightened around the flex will stop the cable being pulled out

Link
http://www.screwfix.com/p/tower-male-comp-gland-white-20mm-pack-of-2/45943

If you use this 1.5mm flex then it may be a good idea to wire the rest of the sockets with the same cable as mixing flex with twin and earth cable (the flat grey stuff) does not give a good connection.
 
I would still over engineer it and use 2.5mm flex for the sake of a few extra quid.
Over engineering / belt & braces approach should always be carried out when dealing with electrics imho, especially when it's only going to cost a little bit extra.
You then don't need to worry about cable factors, volt drop ..etc ..etc

/16th Ed.
 