Hi people,
Just wondering what your view on an APC response to a UPS issue I had. Little back story is a bought a 700VA ups to use just to give my server a chance to shut down when power was lost as we were getting a lot of power cuts, this is rated to around 450W max.
The server has a 650W PSU purely because that is what I had lying around, it runs a low power CPU and a few Hard Drives at 11W max each. It was working fine for about a year (no alarms), until one day poof it would no longer turn on.
I contacted APC support and they said I was at fault because I overloaded the UPS. I called shenanigans but they won't have it as they say they base their sizing on the max possible draw but to me that is a load of rubbish. I had no way of testing the draw /load at the time.
I purchased a 1000VA replacement which is rated to 650W, however this one is more clever and reports the load. So at idle it draws 102W and the max I could get it too by thrashing the disks and running a CPU stress test was 180W Still less than half the original 700VA rating. I responded to APC with my findings and they are adamant they are still correct and it's my fault the UPS died.
I am tempted to push harder as the UPS shouldn't have failed, but am I in the wrong here? Should I have not connected up a 650W PSU to that UPS?
What do you think?
Just wondering what your view on an APC response to a UPS issue I had. Little back story is a bought a 700VA ups to use just to give my server a chance to shut down when power was lost as we were getting a lot of power cuts, this is rated to around 450W max.
The server has a 650W PSU purely because that is what I had lying around, it runs a low power CPU and a few Hard Drives at 11W max each. It was working fine for about a year (no alarms), until one day poof it would no longer turn on.
I contacted APC support and they said I was at fault because I overloaded the UPS. I called shenanigans but they won't have it as they say they base their sizing on the max possible draw but to me that is a load of rubbish. I had no way of testing the draw /load at the time.
I purchased a 1000VA replacement which is rated to 650W, however this one is more clever and reports the load. So at idle it draws 102W and the max I could get it too by thrashing the disks and running a CPU stress test was 180W Still less than half the original 700VA rating. I responded to APC with my findings and they are adamant they are still correct and it's my fault the UPS died.
I am tempted to push harder as the UPS shouldn't have failed, but am I in the wrong here? Should I have not connected up a 650W PSU to that UPS?
What do you think?