Hi Guys
i'm currently testing a lot of old 200um fibres.
but something doesn't add up.
We have 2 big bulkhead cubicles from which we spread out to certain ares.
for these i usually use a launch fibre to get the measurement.
so the launch fibre currently reads in at -10.2dBm
the acutal fibre without the bulkhead measures at -8,5dBm
i later on changed the bulkhead because the reading was too low.
now the measurement for the full length (launch fibre - bulkhead - main fibre) is -14,8dBm.
someone told me i could just subtract the launch fibre measurment from the full measurment but this doesn't add up at all.
could someone be so nice and explain this to me?
thanks