Using all four rings on our electric hob is blowing the fuse.
It has a 13amp fuse in it, should it be higher?
Using all four rings on our electric hob is blowing the fuse.
It has a 13amp fuse in it, should it be higher?
Its a cheap Moffat hob, the model number is worn away.
Yes, it's when all four hobs are on full.
That 13 amp fuse would allow you to connect a 4.2kW appliance. If your hob is rated higher than this then you would need to ensure it is connected to the cooker outlet in your kitchen which should be on a 32A RCD.
I'd be a bit concerned how this cooker is hooked up to the mains as well, if it only has a 13A fuse.
Plug on the end of a bit of 6mm twin lol!
Seen that before!
(Better than a plug on the end of a bit of 1.0mm flex though!)
4.2 KW appliance?
Shouldn't that be a 3.0 KW appliance?
3000 / 230 = 13A