I'm having a weird and annoying issue with an APC smt1500 UPS at a client. Wondering if anyone can give me any tips as APC have not been forthcoming.... This UPS protects all devices at this client: SBS 2011, ADSL modem, firewall, WAP, PBX, switch, USB backup drives etc. The ups has a light load, only around 15% and the monitoring is done on the SBS with PowerChute via USB.
This week I've had 2 graceful shutdowns initiated by the ups, when the client comes in, the trip switch for the server room has tripped - flipping it back and everything comes back on as expected. No problem. On further examination of logs, the mains voltage has been high before the switch to battery. Around 252v. The ups had been trimming throughout the evening.
I've also had 1 non graceful shutdown where all devices appeared to have lost power entirely, without the UPS kicking to battery. Again the client states that the trip to the the server room had been activated, but for some reason, the ups didn't switch to battery and the devices lost power instantly. This is confirmed in the windows logs. Very annoying.
This loss of power without the battery kicking in has happened around 5 times in a year and I'm at a loss to understand why. I'm remote to the client so am very rarely on site (150 miles away), so I have not been able to see the aftermath of one of these occurrences myself. They have all happened in the evening or overnight and have all been preceded by high transfer voltage prior to the loss. The UPS is only a year old and the self tests pass weekly.
I have a feeling that it is a combination of a weird trip switch, high line voltage and something odd in the ups...
Any tips welcome.
This week I've had 2 graceful shutdowns initiated by the ups, when the client comes in, the trip switch for the server room has tripped - flipping it back and everything comes back on as expected. No problem. On further examination of logs, the mains voltage has been high before the switch to battery. Around 252v. The ups had been trimming throughout the evening.
I've also had 1 non graceful shutdown where all devices appeared to have lost power entirely, without the UPS kicking to battery. Again the client states that the trip to the the server room had been activated, but for some reason, the ups didn't switch to battery and the devices lost power instantly. This is confirmed in the windows logs. Very annoying.
This loss of power without the battery kicking in has happened around 5 times in a year and I'm at a loss to understand why. I'm remote to the client so am very rarely on site (150 miles away), so I have not been able to see the aftermath of one of these occurrences myself. They have all happened in the evening or overnight and have all been preceded by high transfer voltage prior to the loss. The UPS is only a year old and the self tests pass weekly.
I have a feeling that it is a combination of a weird trip switch, high line voltage and something odd in the ups...
Any tips welcome.