Have you had the consumer unit tripping? I'm guessing that's your ovens, or some other high drain circuits all twisted in together.
The cable looks like 2.5mm - no different to the ones connected to the 20a mcbs. So that 32A for the three combined isn't giving any protection for a single cable being overloaded - the cable will melt before it trips.
I'd want all those on their own dedicated mcb in a bigger, more suitably sized consumer unit.
Nope, which I suppose is more worrying and explains the melty cables. There is a fair amount going through that MCB, two floors of sockets and a garage. 6 rooms, one being the kitchen. There is a separate circuit for the oven (bloody wants to be), now whether the oven is actually plugged in to it is another matter. We haven't been in here that long, but I'll check later.