I said around a grand, and yes maybe a slight exaggeration, but as you know any decent vac unit will set you back approx £500+ on its own, and then add in the other bits, lines, gauges, leak detectors, etc and you are not far short
Have another read of the 'Code of Practice for Refrigerant Leak Tightness in Compliance with F-Gas Regulations', as issued by the British Refrigeration Association, and also the current actual BSI regulations BS EN 378-1:2016 (updated Dec 2016) they state quite clearly, that for a tightness test the test pressure duration is 24 hours recommended, with a minimum of 6 hours.
Also yes the regulations say Vac to 2 Torr but we all know that any half competent installer will go to at the very least 1 Torr, and most likely if you wish to do your job properly, you would want to be seeing 1/2 Torr or 500 microns ideally, or as damn close to that as you can get, and you would want to see it stable at at that, not fluctuating at all.
Talking of which I have seen a couple of self fit split systems, that get to around 1.0 Torr and appear stable after about half an hour, but after few more mins start to fluctuate, going up to 1.2 and back down to 0.85 then up and down more, this is the moisture boiling off within the system, because of (I can only assume) the poor manufacture and assembly at the factory, and you must wait for that to stabilise before you stop the vac and fill with liquid, so I will vac for minimum 3 hours on any split system, and as I say, really until I see a stable gauge.
Slight aside but I work mainly with large industrial cascade systems, usually using R23 going down to to -60/-80 degrees plus, so am used to working at the extremes, so I guess my tolerances are tighter, and I carry that attention to detail across to fitting split systems as well.
One system I installed last year was a large two stage cascade, with 60 kilos of R404a in stage one, and had around 80 kilos of R23 in stage 2, somewhere around 1200 metres of pipework within the system, almost 500 brazed or silver soldered joints, had that on tightness test for eight weeks, and then on vac pump for nearly a month before finally reading stable at 0.6 Torr to add the refrigerant, but as I say that is an extreme.