Rule of thumb to vent a system is to do it with the pump turned OFF. With old systems (like your gloworm) this is important because you will have positive and negative sides of the system. And it can easily be the case to vent a rad, hear some 'hissing' and think "wow look at all the air I'm venting" when infact the rad is sucking air IN! Because of the negative side of the pump.
Modern fully pumped systems arent as bad and you can use the positive side (run the pump) to assist venting.
But sealed sytems (modern) should definately NOT be be run until properly filled, vented and pressurised.
mysticsniper
Start from the beginning mate
Get you ass in the loft and check both tanks have water in them and that the float valves operate.
Turn your system off
Open all your rad valves (not lockshield/ capped end)
Vent the rads starting with downstairs and working your way upstairs.
Make sure you get water out of all the rads.
Turn your system ON
If some rads get hot and others dont, then turn the hot ones OFF, and see if heat gets into the cold ones.
Possible problems:
Stuck float valve: no water in cold feed & expansion tank: DIY
blocked cold feed: tank full but cant get rads filled. Plumber
pump tired: system full but pump can only get a couple rads warm, (depends which rads you have turned on): Plumber or good DIYer
Pump & valves blocked with sludge and scale, happens on old systems: Plumber
**Motorised valve faulty: not opening or rotted rubber inside (Honeywell), Whole valve: Plumber. Synchron or head, Plumber or good DIYer
** If you have one.
Me off to work now
Have fun
Modern fully pumped systems arent as bad and you can use the positive side (run the pump) to assist venting.
But sealed sytems (modern) should definately NOT be be run until properly filled, vented and pressurised.
mysticsniper
Start from the beginning mate

Get you ass in the loft and check both tanks have water in them and that the float valves operate.
Turn your system off
Open all your rad valves (not lockshield/ capped end)
Vent the rads starting with downstairs and working your way upstairs.
Make sure you get water out of all the rads.
Turn your system ON
If some rads get hot and others dont, then turn the hot ones OFF, and see if heat gets into the cold ones.
Possible problems:
Stuck float valve: no water in cold feed & expansion tank: DIY
blocked cold feed: tank full but cant get rads filled. Plumber
pump tired: system full but pump can only get a couple rads warm, (depends which rads you have turned on): Plumber or good DIYer
Pump & valves blocked with sludge and scale, happens on old systems: Plumber
**Motorised valve faulty: not opening or rotted rubber inside (Honeywell), Whole valve: Plumber. Synchron or head, Plumber or good DIYer
** If you have one.
Me off to work now
Have fun