I thought legally you had to be a certified electrician even to work on your own electrics now?
Only for Kitchen and Bathroom I think.
You can always do it yourself and get an electrician to sign it off.
I thought legally you had to be a certified electrician even to work on your own electrics now?
Only for Kitchen and Bathroom I think.
You can always do it yourself and get an electrician to sign it off.
Continuity tested. Found a fault due to a problem with one socket also. Used a socket tester on all new sockets. Checked bonds also. Have used a fly earth lead for cpc on the new sockets, I was't going to rely on the screws!!
As far as i know, the home DIY'er is allowed to replace sockets, switches and light fittings and that's the limit. If he wants to add/modify a circuit he must get a sparky in.
So that's a no then lol. No IR test or a ZS test to see if there is a real path to earth. RCD test? (They are protected by an RCD I take it)
DIY Electrics are a nightmare tbh. Laws are there for a reason to let the competent people who are trained take care of things and take responsibility for the circuit or installation.
I'm not saying you have done a bad job installing and the circuits are doomed to fail. Without proper testing of the circuits you can not be sure though.
Continuity tested. Found a fault due to a problem with one socket also. Used a socket tester on all new sockets. Checked bonds also. Have used a fly earth lead for cpc on the new sockets, I was't going to rely on the screws!!
Assume by a socket tester you mean a martindale kind of device with the 3 lights on the front? If so STOP using it, they cannot distinguish a neutral/earth reverse
This one? [img ]http://www.sercal-testequipmentsale...ages/fluke-sm100-socket-master-basic-12-p.jpg[ img]
Read the bottom line on it
I cannot see how any plug in socket tester could detect a neutral earth reversal (at least not on a TN system), such a fault should be picked up using dead tests