Soldato
- Joined
- 27 Mar 2004
- Posts
- 4,645
- Location
- Telford
any heating engineers here?
just after a bit of advice regarding radiator size
my bedroom does not get warm enough in the winter
if the heatings on for 3pm and its very cold outside it does not get warm till around 8-9pm rest of the house is fine (when the radiators are on)
so i am looking at replacing the current radiator with a bigger one
room is roughly 29 meters squared
roughly 3m long 4m wide 2.4 high, 2 small double glazed windows and 1 full outside wall
current rad outputs around 3200 btus (single panel single convector)
according to my measurments i need a rad outputing 4500 btus
but i am thinking of putting a bigger rad in (5400 btus) double panel single convector
and controlling it with a thermostatic valve
is this an ok way of doing things or would it be better to put in a rad of around 4500 btus?
and hope this will be enough?
current rad is 1120 wide and 500 high
will be going to use a double rad single convector (1120 x 600)
hope that makes sense
just after a bit of advice regarding radiator size
my bedroom does not get warm enough in the winter
if the heatings on for 3pm and its very cold outside it does not get warm till around 8-9pm rest of the house is fine (when the radiators are on)
so i am looking at replacing the current radiator with a bigger one
room is roughly 29 meters squared
roughly 3m long 4m wide 2.4 high, 2 small double glazed windows and 1 full outside wall
current rad outputs around 3200 btus (single panel single convector)
according to my measurments i need a rad outputing 4500 btus
but i am thinking of putting a bigger rad in (5400 btus) double panel single convector
and controlling it with a thermostatic valve
is this an ok way of doing things or would it be better to put in a rad of around 4500 btus?
and hope this will be enough?
current rad is 1120 wide and 500 high
will be going to use a double rad single convector (1120 x 600)
hope that makes sense
Last edited: