Stupid light wiring question!

Associate
Joined
10 Feb 2006
Posts
882
Location
Nottingham
I've changed many lights, switches etc. in the past but am completley stumped regarding this one! (and feel stupid for not figuring it out). I've tried many combinations but think I need to take time out before I scream. The light currently works but neither switch does.

I have a room with a Light, Single light switch on wall and a pull cord.

So to replace these I bought:

Light (standard hanging lantern)
Single switch (2 way)
Pull cord switch (2 way)

The following wires are present at each point:

Light:

3 seperate feeds...
Feed 1 : 1 Red and 1 Black wire.
Feed 2 : 1 Red and 1 Black wire.
Feed 3 : 2 Red wires.
+ Earth.


Light switch on wall:
1 Yellow wire, 1 Red wire and 1 Blue wire.

Pull cord:
Believe coming from 3 feeds also but hard to tell (wiring is in a mess).
In total there are 3 Red Wires,
1 Blue Wire,
1 Yellow Wire
and Earth.


Be gentle!
 
Yeah, can't find a diagram that matches the correct number/colour of cables I have at each point. The diagrams that came with the switches again don't match the combination of wires I have.
 
At a guess

switch - anything will do... yellow, blue, red - common, L1, L2 etc
Copy this at pullcord but add 1 of the extra reds into L1 and the 2nd extra red into L2

Now at light fitting the 2 red and black feeds are probably live and neutral and the 2 red are probably switch live and perm live going to the pull cord

so 2 blacks into neutral terminal
2 reds (from same cable as blacks) + 1 red into live terminal
1 red into switch live terminal

Try this should work, Otherwise need to get a multimeter out maybe
 
Last edited:
Good luck. I had to deal with this when I rewired my socket:

UDKcF12.jpg
 
At a guess

switch - anything will do... yellow, blue, red - common, L1, L2 etc
Copy this at pullcord but add 1 of the extra reds into L1 and the 2nd extra red into L2

Now at light fitting the 2 red and black feeds are probably live and neutral and the 2 red are probably switch live and perm live going to the pull cord

so 2 blacks into neutral terminal
2 reds (from same cable as blacks) + 1 red into live terminal
1 red into switch live terminal

Try this should work, Otherwise need to get a multimeter out maybe

This should be correct.


To the photo above.. That's pretty easy :p. Actually changed two switches like that today. (Top and bottom of stairs)
 
At a guess

switch - anything will do... yellow, blue, red - common, L1, L2 etc
Copy this at pullcord but add 1 of the extra reds into L1 and the 2nd extra red into L2

Now at light fitting the 2 red and black feeds are probably live and neutral and the 2 red are probably switch live and perm live going to the pull cord

so 2 blacks into neutral terminal
2 reds (from same cable as blacks) + 1 red into live terminal
1 red into switch live terminal

Try this should work, Otherwise need to get a multimeter out maybe

Worked perfectly. Thank you!

Now on to the skirting!
 