I've got a Vaillant Eco TEC Plus 831, installed last year. I'm playing around with temps. It was set by the engineer at 60c target temp for water, and 60c for the rads.
The water always gets nice and hot. I was watching the blue display readout on the boiler as I ran the kitchen tap and it reached 70c. Why would it reach 70c with a target of 60c? I'm happy with the temperature but not sure why it goes 10c over the set temp.


The radiators are all on at the moment, newly installed at the same time as the Vaillant. They're all pretty hot now but I can easily keep my hand on them at 60c. That however doesn't go over the target temp. So I just increased the boiler temp to 70c for the rads. It's maximum goes to 75c. Now the rads feel just right, almost too hot to keep my hands on for too long. Does 70c seem right or too high? I set the thermostat (Salus RT500RF) to 23c and currently the room temp has reached 20c. I presume the higher I set the boiler temp, the faster I can achieve the selected room temp?
 
Last edited:
Associate
Joined
17 Oct 2010
Posts
493
Location
Welling
all your assumptions are correct provided your radiators are adequately sized and your home has good thermal efficiency. You can set the boiler to 80c but if the rads are too small and the building has poor thermal properties then your rooms either will not achieve the desired temperature or it will take forever to get there.

around 70c is fine for the rads. The temp for your hot water seems high but that's down to personal preference. i always recommend around 50c.
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
all your assumptions are correct provided your radiators are adequately sized and your home has good thermal efficiency. You can set the boiler to 80c but if the rads are too small and the building has poor thermal properties then your rooms either will not achieve the desired temperature or it will take forever to get there.

around 70c is fine for the rads. The temp for your hot water seems high but that's down to personal preference. i always recommend around 50c.

It's quite a cold and old house tbh. Even with my new double glazed upvc windows in all the rooms and the rads at 70c, the thermostat is still showing 20.5c in my bedroom and the heating indicator still flashing on the thermostat, so yea, the thermal properties of the building are presumably not very good. Yeah, I think it IS going to take forever to reach 23c that I selected 2 hours ago.
 
Associate
Joined
17 Oct 2010
Posts
493
Location
Welling
well there's your answer. are they cavity walls or solid? you can get cavity wall insulation and loft insulation done for free in certain places.

are the rads old or new?
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
well there's your answer. are they cavity walls or solid? you can get cavity wall insulation and loft insulation done for free in certain places.

are the rads old or new?

It's an edwardian terraced house so solid 9 inch walls I believe.

The 4 rads, heated towel rail and the Vaillant Combi are new, installed a year ago. The rads were only used sparingly for the first time last winter and then last night for the first time since January.
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
Hi guys, I've got some questions about servicing the Eco TEC Plus 831.

A gas safe registered central heating engineer installed my central heating (4 rads, towel rail and combi boiler) about November last year and said Vaillant would contact me about a service. Should be about £90 to £100 I think he said. Is that too expensive, is it worth me getting anyone else other than Vaillant to do it? The engineer was going to service it himself for around £80 to £90, but we sort of fell out with each other since so I can't really get him to do it now I don't think, he never answers my calls.

Haven't heard from Vaillant yet, is it absolutely vital I contact them and have it done and would it void my 7 year warranty if a service isn't done? But even regardless of warranty, does a year of usage on a quality brand like Vaillant mean that it might be less important to service it before 2 years?

Haven't used the central heating that much, just a few weeks last winter and that was only the heated towel rail and one or two other rads now and then.
 
Soldato
Joined
19 Jan 2010
Posts
6,769
Location
South West
Valiant boilers come with 7 year warranty,(can't remember) it only remains valid if you use a Valliant approved engineer for servicing & you have the boiler serviced regularly.

So, if the boiler went wrong (most unlikely), you might up end up with a expensive repair bill, if Valliant don't honour the warranty.
 
Soldato
Joined
22 Jun 2004
Posts
2,692
Location
South Scotland
I've got a Vaillant Eco TEC Plus 831, installed last year. I'm playing around with temps. It was set by the engineer at 60c target temp for water, and 60c for the rads.
The water always gets nice and hot. I was watching the blue display readout on the boiler as I ran the kitchen tap and it reached 70c. Why would it reach 70c with a target of 60c? I'm happy with the temperature but not sure why it goes 10c over the set temp.


The radiators are all on at the moment, newly installed at the same time as the Vaillant. They're all pretty hot now but I can easily keep my hand on them at 60c. That however doesn't go over the target temp. So I just increased the boiler temp to 70c for the rads. It's maximum goes to 75c. Now the rads feel just right, almost too hot to keep my hands on for too long. Does 70c seem right or too high? I set the thermostat (Salus RT500RF) to 23c and currently the room temp has reached 20c. I presume the higher I set the boiler temp, the faster I can achieve the selected room temp?

I have the same boiler, remember it wont condense properly (and be its most efficient) if your return flow temp is above 60 ish, (google will confirm) currently I`m running it for CH at 58 I think, but when it gets really cold will increase that as performance is obviously less.
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
I have the same boiler, remember it wont condense properly (and be its most efficient) if your return flow temp is above 60 ish, (google will confirm) currently I`m running it for CH at 58 I think, but when it gets really cold will increase that as performance is obviously less.

Thanks, I'll keep that in mind.

Valiant boilers come with 7 year warranty,(can't remember) it only remains valid if you use a Valliant approved engineer for servicing & you have the boiler serviced regularly.

So, if the boiler went wrong (most unlikely), you might up end up with a expensive repair bill, if Valliant don't honour the warranty.

Yeah, mine has a 7 year warranty. So is up to a £100 for a service about right?
 
Associate
Joined
23 Oct 2006
Posts
939
Location
Lincoln
I have the same boiler, remember it wont condense properly (and be its most efficient) if your return flow temp is above 60 ish, (google will confirm) currently I`m running it for CH at 58 I think, but when it gets really cold will increase that as performance is obviously less.


Is there a way to measure the return temps to the boiler to get it set right?
 
Soldato
Joined
22 Jun 2004
Posts
2,692
Location
South Scotland
Is there a way to measure the return temps to the boiler to get it set right?

I think you would just use a thermometer, I know you get thermometers specifically to measure the fall in temp across radiators , this is important to balance your system correctly, worth doing. I would assume one of these would do it. Atm I just do it by hand......set my flow temp to 58 or so and feel the return pipe and if its significantly cooler I assume it must be in the ballpark. This kinda thing would do it LINK

As temps drop/change though unless you have a weather compensator fitted you would need to be tweaking the flow temp manually to get the desired/most efficient return temps, def worth getting return temps as low as you can tho it seems.

Weather compensators (as far as I can understand) will modify the flow temp as the outside temps change, seems a really good idea, think the one for Vaillants are about £120
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
Just found my benchmark checklist. http://i.imgur.com/DaLCOyj.jpg

Seems I'm premature as it's commissioned 11th Jan this year, even though the system was installed around November. So the 7 year warranty began in January. I've just arranged a service for 10th Jan in the morning with a gas safe engineer. £65 inc VAT, which is excellent. Apparently takes 30 to 45 minutes.
 
Soldato
Joined
19 Jan 2010
Posts
6,769
Location
South West
Just found my benchmark checklist. http://i.imgur.com/DaLCOyj.jpg

Seems I'm premature as it's commissioned 11th Jan this year, even though the system was installed around November. So the 7 year warranty began in January. I've just arranged a service for 10th Jan in the morning with a gas safe engineer. £65 inc VAT, which is excellent. Apparently takes 30 to 45 minutes.

My gas engineer plugs a flue analyser tester in, it then runs through a program of various tests.
He does a few other tests for carbon monoxide, flue,etc, & he gone in 30 minutes.

But, some engineer's do a more in depth service after several years, mine got it's first complete strip down after three or four years, flue analyser tester came back 100% every year, just engineer wanted a more in depth inspection of the burner this year.


See this link.


http://www.youtube.com/watch?v=6lF5O_bWrkQ
 
Last edited:
Soldato
Joined
22 Jun 2004
Posts
2,692
Location
South Scotland
Just found my benchmark checklist. http://i.imgur.com/DaLCOyj.jpg

Seems I'm premature as it's commissioned 11th Jan this year, even though the system was installed around November. So the 7 year warranty began in January. I've just arranged a service for 10th Jan in the morning with a gas safe engineer. £65 inc VAT, which is excellent. Apparently takes 30 to 45 minutes.

interesting to see the temp drop, gives us a ballpark estimate as to how much it drops, how many rads?
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
My gas engineer plugs a flue analyser tester in, it then runs through a program of various tests.
He does a few other tests for carbon monoxide, flue,etc, & he gone in 30 minutes.

But, some engineer's do a more in depth service.

See this link.


http://www.youtube.com/watch?v=6lF5O_bWrkQ

Cheers, I'll watch that in a bit. The guy coming mentioned he does a CO test, and I'm guessing he'll do most of the other things you mentioned.


interesting to see the temp drop, gives us a ballpark estimate as to how much it drops, how many rads?

I've got 2 single and 2 double rads and a heated towel rail. As I'm a bit clueless, I don't understand what you mean by my temperature drops.
 
Soldato
Joined
22 Jun 2004
Posts
2,692
Location
South Scotland
I've got 2 single and 2 double rads and a heated towel rail. As I'm a bit clueless, I don't understand what you mean by my temperature drops.

Apparently these condensing boilers only achieve their claimed efficiency if the flow return temp is below 55 degrees, Google this and you will find loads. Essentially you want the return temps as low as you can get them (I think), this though I think will be difficult as when it gets colder you will need to up the temps to get adequate performance.

Flow = newly heated water coming straight out of boiler to radiators.

Return = water coming back to boiler after going round the radiators.
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
Apparently these condensing boilers only achieve their claimed efficiency if the flow return temp is below 55 degrees, Google this and you will find loads. Essentially you want the return temps as low as you can get them (I think), this though I think will be difficult as when it gets colder you will need to up the temps to get adequate performance.

Flow = newly heated water coming straight out of boiler to radiators.

Return = water coming back to boiler after going round the radiators.

Ah, ok. I'll look into.


I'm a bit confused now about the servicing. I'm mostly doing this to keep the warranty valid. I posted on another forum that has professional engineers, and one of them said,

"For £65 you won't be getting a service. What you'll have is an inspection to see if it needs a full service. A service would mean a new seal worth £20, draining the appliance to check/recharge the expansion vessel and a clean out of the trap as well as all the safety checks. I don't doubt filling the service record is all you want, and he'll fill it in, but if your burner seal gives way or main heat exchanger leaks as a result of not having the full service, the only thing Vaillant will offer is an expensive repair or monthly subscription.
I advise customers to have a full service initially then short services/inspections for one or two years in between
."

When I contested him on this, he was curt and basically replied that is what is needed and that he knows what servicing involves and I don't.
So how come when I booked my service, I wasn't told for £65 I'd be getting a pre-service inspection, not a full service? As far as I'm concerned, I'd booked the boiler to be serviced, and if there's nothing wrong with it, I just pay £65 and the warranty is valid. Now that doesn't seem to be the case. So now I'm wondering if I have to spend more and get this seal done and draining of the expansion vessel, regardless if it needs it or not, or, if the inspection would show these things up anyway and if he determines if they need doing? Anyone know? :confused:
 
Soldato
Joined
1 Jan 2003
Posts
2,968
Location
Derbyshire
This is because manufacturers of modern boilers are trying to cut down on the maintenance required for the upkeep of their boilers. Annual strip down of a boiler ads wear and tear to the thing, and in a lot of cases requires seals to do the job, at an extra cost. And time!

So, functional, visual and safety tests are done on the appliance, and a gas analyser reading is taken to assess whether a strip down and full service is required. If not, jobs a good un, pay your money, get the paperwork filled in, and go away with the peace of mind that the boilers ok and the warranty is kept up :)

Mick
 
Associate
Joined
17 Oct 2010
Posts
493
Location
Welling
I'm gonna address a few issues here.

1. As flyingfish said, removing the burner and inspecting the heat exchanger is only necessary if the combustion analysis comes back with poor readings which if your system is only a year old it won't. might be worth it on the 3rd service though.

2. you don't have to use a vaillant registered engineer to service your appliance in order to maintain your warranty. Any gas safe engineer can do it. As long as your logbook is filled in it will be fine.

3. It should cost you no more than £70+vat for a service.

4. On an average heating system, the Delta T is usually around 10c. Therefore set your boiler flow temp to around 65c and it'll be close to it's most efficient.
 
Soldato
OP
Joined
17 Aug 2009
Posts
17,823
Location
Finchley, London
Thanks FlyingFish and justalex. Sounds good to me.

Sorry to be over cautious, but just for arguments sake and further clarification on this point that guy made to me:

"if your burner seal gives way or main heat exchanger leaks as a result of not having the full service, the only thing Vaillant will offer is an expensive repair or monthly subscription."

So, if the engineer comes and does his functional, visual and safety tests and determines from good combustion analysis readings that a full strip down/full service/heat exchanger test and seal replacement isn't necessary, he'll fill in the service record and the warranty remains valid.

What happens though if the burner seal DOES later on decide to break or the heat exchanger leaks a few months later, even though a full service was determined not to be needed. Are Vaillant still obliged to honour the warranty and repair for free, or will they say I didn't have a full strip down service and didn't replace the seal and charge me to fix it?
 