Calculating current (A) for electrical cables
6 Feb 2004
Norfolk Broads
I need to run some cable before I complete some building work.
If I know the current that the cable will carry I can look it up in my handy little table and it will tell me what size cable to lay. Problem is I don't know the current. The only reference I have is that my 220Kw three phase supply (at 380V) comes in on a 240 sq. mm four core cable.
I do know that the load is a 3 phase motor (Star Delta job, not sure which but I know the motor has a soft starter) which is rated at 30 Kw at 380V (not in UK by the way). The power factor is 0.8 (genset in use here).
I'd really like to see the formulation rather than just the answer as I have a few more cables I need to run (all three phase loads) for loads ranging from 5-42 Kw.
TIA
Off the top of my head:
You need to know the current in each phase.
Phase voltage = Line voltage / Sqrt(3) [On primary (star) side]
Phase voltage = 380V / (sqrt(3)) = 219.4V
Power = 10kW per phase
Current per phase = power per phase / (phase voltage x power factor)
= 10000 / (219.4 * 0.8) = 56.97A
So you will need a 57A cable for each phase.
I'm assuming the 'soft start' thing means your motor is not going to have a large inrush current. Even if you do have inrush the cable will have a cyclic rating that will allow a temporary over-current without burning out.
Don't quote me on this stuff though.
You are working with a 220kW supply and you don't know how to work out the amps?
I'd suggest getting a qualified electrical engineer to do the work. There are many things you need to be aware of when working with 3-phase power.
I am a qualified electrical engineer.
I need to lay a cable as I'm doing some building work. Obviously you didn't read the post as I simply want to run the cable, I never said anything about connecting it. Now bugger off and annoy someone else, there's a good boy ;)
There's no need for the childish and derogatory comments. This is not your forum and it is not your place to tell other members to bugger off.
Remember that there is more to it than selecting a cable capable of carrying the load, volt drop (so you arn't loosing too much power in cable looses) and disconnection time (in the event of a phase to earth fault the current that flows must be sufficent to operate the over current device within a set amount of time) and protection against short circuit (if there is a short circuit, the cable must be able to withstand the let through energy of the protective device)
I'm looking at it from a prospective of british regs (BS7671), you should check your local regs.
That said, my starting point would most likely be 16mm² SWA on a TP C63 then you do the relevant calculations and decide whether its right, or whether it needs 'tweaking'
If this is a commercial installation, shouldn't you be getting electricians in to lay the cable?
We get electricians to do ALL our cables, from 240V single phase to 20+KW three phase. If we don't, we're not insured.
unless you have the full spec of the load , type of starter , type of load ( is it a fan or pump ) will it be on full load at start,
then we have the cable type SWA , mineral insulated , multi core , single core trifoil ,in a duct , in air and ambient tempreture
it is very difficult to size the cable
its only a 40 hp tiny realy bit of wet string would be ok :D
volt drop is (Ro * L) / A
0.8 pf for I assume an induction motor is very high I would have said 0.6 lag would have been nearer
There are no local regs here! :p I am the local regs! If the sparkies here had their way they would use 2.5mm and twist it together ;)
When I first put the equipment in there was a local "electrical contractor" that came to spec up my requirements, I was offerred a choice of 4 core SWA XLPE 10mm or........4 core SWA XLPE 10mm, why? Because that was all they had in stock! I ordered the cable myself from Singapore and shipped it up, that was 8 years ago (and crossing fingers :p ) and I've never had a problem.
I recall a couple of years ago I found an online cable selection calculator, you entered all the variables (ambient temp, cable length, voltage, current etc) and it would work it all out for you. I know I have to de-rate the cable on ambient temp alone. I appreciate what you're saying about voltage drop, I've managed to find a spreadsheet on the net which takes care of that.
Interestingly it's pointing at 16mm :)
MrMatteh said:
tyler durden style?
It got too expensive, we had to shift to using palm oil :D
There is no insurance here (and I'm really not joking!) ;) There's no H&S either. A qualified electrician is defined as "an individual who can make a lightbulb work without getting fried in the process".