Don't forget radiators are rated at a Delta 50c which isn't really efficient for a modern condensing boiler.
Bigger radiator the better there are no functional downsides to getting the biggest radiator that will fit in the room.
Delta 50c is 80c flow, 60c return and 20c room temp.
Therefore 70c radiator temp. 70-20=50c.
Condensing boilers prefer return to be less than 55c. So you can see why delta 50 is a bit rubbish.
My house is based around delta 30.
60 flow, 40 return, 50 rad temp. It often far exceeds this though, very often the flow temp will be 30c or less.