Combi boiler cutting out while running hot water

Soldato
Joined
29 Sep 2003
Posts
5,826
Location
Newcastle upon Tyne
Hi all

When I run a hot tap the combi boiler fires up and heats the water. However, as the pressure drops, the boiler switches off and stops heating the water. I'm left with just cold water coming from the hot tap. I can force the boiler to start heating the water again by turning the tap on some more, but at this point I'm pouring quite a considerable amount of water down the drain.

Does anyone know why my boiler might be shutting off heating the water despite the fact that it is still running?

I should note that the heating works fine and that the boiler has sufficient pressure in the heating system (1 bar).

Many thanks

M.
 
Last edited:
I would say your combi is a little old and is not a modulating type so the gas burner is either on or off with no 'throttle' if you will. If you are running the water slowly then its likely that the temprature of the water is exceeding what the boiler will allow and if it cannot modulate then the only thing it can do is shut off to protect the boiler from actually boiling and you lot from scalds from very hot water.

You should be able to find out if its modulating with the help of google quite easily or pop the model in here and I'm sure someone will help you find out.

Bit of a guess really.


Oh while I think of it there is a pressure switch in the boiler too on the cold water feed side so that if there is insufficient flow it will shut the boiler off for the above reasons.

More I think of it the more it sounds like a boiler design "feature"

It's a Baxi Combi 105HE.
 