Inverter Farked??

Associate
Joined
25 Nov 2017
Posts
352
Hello,

I'm after some advice on my inverter, from those who know about them!

I have a Sunnyboy 2500 HF that is connected to 13 x 240w panels.

The system seems to have been installed in 2012 by the previous owner (so out of warranty).

I don't look at the inverter often, only really grabbing a meter reading every quarter when asked to by the FIT provider.

When i looked yesterday however, my spider sense suggested the inverter may not be behaving as it should (noting it was early evening when I looked).

So what seems to be wrong?

First the inverted has 4 LEDs on it. From the instructions it should have a solid green light when generating power and a flashing green light when awaiting sufficient illumination to begin generating. Or a solid red light when there is an error. It has no lights whatsoever illuminated.

The main LCD works however and does show the firmware details etc when engaged. Oddly however, it showed no power generation nor any for the current day (it had been sunny).

In the last 24 hours (mostly overcast). There has been no power generation what so ever.

So the lack of any LED being illuminated and the lack of any power generation in the last 24 hours, and a lack of a "day" generation reading for a sunny day does make me suspect that there is an issue...

What does the forum think?

If the answer is, I need a new inverter - a there any recommended companies to contact? I am wiltshire based if that makes any odds.

Thanks.
 
Associate
OP
Joined
25 Nov 2017
Posts
352
Yes. Thanks. I did download a copy of the manual and have a printed one left by the previous occupants.

The manual is a bit thin however and does not really have any troubleshooting guidance.

The manual suggests with no sun on the panels you should see a green flashing light. However I have seen a youtube video, which suggests at nighttime there would be no lights visible. I suspect the youtube statement is inaccurate, but I was hopingto hear from someone with direct experience and knowledge.
 
Soldato
Joined
18 Oct 2002
Posts
14,218
Location
West Midlands
If it is faulty don't just assume it will be cheaper to repair it than replace it, 4KW inverters can be had for under £450, and you'll get a decent warranty with a new one. Plus some of the older inverters were terrible, so maybe better replacing it if it turns out to be faulty.
 
Associate
OP
Joined
25 Nov 2017
Posts
352
If it is faulty don't just assume it will be cheaper to repair it than replace it, 4KW inverters can be had for under £450, and you'll get a decent warranty with a new one. Plus some of the older inverters were terrible, so maybe better replacing it if it turns out to be faulty.

Hi, yes, that does seem to be the common view. Also seems that the model I have often fail after 5 years. So looks like I may soon be patting with around £750. But annoying as I am looking to sell the house soon... but I guess working solar will be attractive to future buyers.
 
Soldato
Joined
28 Dec 2017
Posts
8,500
Location
Beds
How come we've all assumed the issue is the inverter, not the bank of panels or connection? Am I missing something?

FWIW we have a pair of 1200W Sunnyboy units and they only power up at all once there's some daylight. Then there are 3x LEDs which effectively indicate the stages of light up until normal generation. So aside from the display on your unit, I would take "no LEDs" to mean possibly no PV feed.
 
Man of Honour
Joined
13 Oct 2006
Posts
91,408
Generic brand (and even many better brand) inverters only tend to last around 10 years of decent usage.
 
Associate
OP
Joined
25 Nov 2017
Posts
352
How come we've all assumed the issue is the inverter, not the bank of panels or connection? Am I missing something?

FWIW we have a pair of 1200W Sunnyboy units and they only power up at all once there's some daylight. Then there are 3x LEDs which effectively indicate the stages of light up until normal generation. So aside from the display on your unit, I would take "no LEDs" to mean possibly no PV feed.

Fair point. It could be no input voltage. Not totally sure how I would check that on the system..
 
Associate
OP
Joined
25 Nov 2017
Posts
352
Measure the MC4 connector input voltage using a DVM. Easy to do, plenty of guides online if you are unsure.
Thanks. Looks doable. I did try taking the cover off of the DC isolator switch to measure there, but the cover did not want to come off easily, so I did not chance it.

Would you happen to know if the MC4 connections are push fit (thus just pull out) or if they are twisted in? I don't want yo break anything.

Thnaks
 
Associate
OP
Joined
25 Nov 2017
Posts
352
OK. So seems that the mc4s are push fit and a little screw driver can prise them open.

So I turned off the ac and dc power and the fuse board for good measure.

Took the bottom black panel off of the inverter (the unit with thr fan).

I opened up the mc4 connectors, turned the dc isolater and fuseboard back on...

Applied the multimeter probes, and could not get a dc voltage reading. I had check the meter using a 1.5v battery, so seems I had the correct setting for dc.

So either no power is coming from the panels or I am testing wrong...
 
Soldato
Joined
28 Dec 2017
Posts
8,500
Location
Beds
Applied the multimeter probes, and could not get a dc voltage reading. I had check the meter using a 1.5v battery, so seems I had the correct setting for dc.

So either no power is coming from the panels or I am testing wrong...
Make sure you're ranging the meter right - IIRC solar panels can deliver up to 175V DC so definitely start on your highest setting.
 
Associate
OP
Joined
25 Nov 2017
Posts
352
Yeah. Set the meter to 600v dc, and also inserted some 6mm wire into the connectors (as my multimeter probes are not very long). Still nothing...

Guess it is time to get someone in!
 
Associate
OP
Joined
25 Nov 2017
Posts
352
Managed to test the voltage across the DC isolator.. nothing. So clearly an issue with the panel array, not the inverter.

Learning point for the day... the switch on the isolator box needs to be in the off position for rhe cover to come off... previous I had it in the on position, hence why I could not open the box!
 