Kitchen electrics DIY'able after April?

Associate
Joined
19 Sep 2007
Posts
420
Planning a new kitchen and will be replacing a freestanding cooker with single oven and hob. I plan to use the existing cooker connection unit and a dual outlet plate that will feed the hob and a fused spur for the oven. Also plan on extending the ring main for a extra couple sockets.

All pretty straight forward but from April 2013 the kitchen is no longer notifiable under part p? Am I free to DIY?
 
It's good practice to run a separate circuit for each, better than spurs.
I was old school trained, & my instructor warcry was any appliance rated at 2Kw or higher should have its own circuit.

But a lot of people now use a 45amp Dual Appliance Outlet Plate http://www.cef.co.uk/catalogue/products/335211-45a-easyfit-dual-appliance-outlet-plate
But, you will need to have 10mm T&E feed from the comsumer unit & 45a fuse, if you currently have 6mm T&E & 32a fuse, it's too close to load capacity limit allowing diversity.

Part P work included adding a new circuit (your cooker) & alterations hazardous locations kitchens, bathrooms,outdoors, but your correct in the other changes in April this year.

http://www.niceic.com/Uploads/File8952.pdf

But,it dosen't cover alteration to existing circuits in a special location, ie your kitchen cooker, so I would consider it notifiable work.
 
Last edited:
Ah I thought the only location would be the bathroom after april. The cooker is currently fed from a 6mm cable but I plan on putting a single oven and ceramic hob in so the load shouldnt be much different than the freestanding one.

Someone has put a 2.5mm cable on a radial for the washer, tumble drier and extractor with a 16a breaker, the plan is to move it and have it below the counter top and then extending the ring thats only feeding the fridge and kettle at minute and add another socket above the work top.

I do work with an electrician now and again so im going to pinch him next time he's local.

Unless I'm wiring a new circuit to the consumer unit or tinkering in the bathroom my impression was your free to do as you please from April.
 
Last edited:
Always had oven & hob all in one, but I been thinking about seperates, last week I was looking at a Bosch hob & was shocked at it's rating of 6.6Kw, & a single built in oven at 3Kw, glad I put in that 10mm cable now.
 