To save starting a new thread, if you have a friend who has around 6kw of stuff to power in a single room, is it best to try and split the load between ring circuits?
He;s a mobile DJ who has around 3kw of lights, and also around 3kw of soundsystem to power... and it can be a pain to try and power it all.
The only thing I don't know how to do is determine is if 2 wall sockets are on the same ring, it's there some sort of plug tester type device avaliable?
Ideally you'd want to run a new dedicated radial circuit to it from the consumer unit, similar to that for an immersion heater, shower or cooker and stick some 40a protection on it as 6kw is pushing it for the 2.5mm cable on the ring (depending on it's length) and the draw is @26amps alone.
If the sockets are in the same room then it's highly likely they are on the same ring, or one spurred off the other. Looking at the consumer unit will tell you if there is more than 1 ring in the house (usually upstairs and downstairs separated) and simply switching each ring off in turn with someting connected to the sockets in question will determine what's what.

Edit: If there is an upstairs and downstairs ring you could split it between those with a decent extension...



13amp extension, which also states max load at 230V, works out at just under 3k/w!! 