That number on your boiler is more the hot water, central heating uses less.

Ok, so assuming I had the same boiler as the OP which is 24kw, then it can power 88btu's of hot water and central heating?

Do I just assume it can pretty much power as many radiators as I want? But the hot water would suffer if we were to try and shower at the same time?

Just trying to get my head around it.
 
Ok, so assuming I had the same boiler as the OP which is 24kw, then it can power 88btu's of hot water and central heating?

Do I just assume it can pretty much power as many radiators as I want? But the hot water would suffer if we were to try and shower at the same time?

Just trying to get my head around it.

Any boiler size will be fine for the central heating of normal size houses.
a 32kw boiler still tops out at 24kw give or take for central heating.
The larger the boiler the better for hot water demand, ie a shower. But the downside is they modulate higher as well so when the central heating only needs a few kw it might only be able to go down to around 8kw for a 32kw or 4kw for a 24kw boiler, which decreases effiecency as a boiler prefers to be on for sustained periods rather than on and off all the time. So balance your needs between hot water demand and central heating efficiency.

Its closer to 82BTUs as well, but ignore that, use kw.

On radiators make sure you understand where the kw rating comes from before buying any.

There specced to delta 50c, which is too high for a condensing boiler.
The rating presumes a flow of 80c, return of 60c. You want delta 40c minimum.

The manufacturer will have the calculation you need to apply but it will roughly be 0.75 so a 2kw radiator is better suited as a 1.5kw radiator when used with a condensing boiler.

Im doing my house at a delta 35 to further ensure the boiler is running at peak efficiency and also to improve warm up times on cold mornings. For 35c its 0.63 so the 2kw becomes 1.2kw.

As you can see you soon need much larger radiators. There is no downside other than space required for going bigger on radiators.

I hope all that makes sense.
 
Last edited:
Any boiler size will be fine for the central heating of normal size houses.
a 32kw boiler still tops out at 24kw give or take for central heating.
The larger the boiler the better for hot water demand, ie a shower. But the downside is they modulate higher as well so when the central heating only needs a few kw it might only be able to go down to around 8kw for a 32kw or 4kw for a 24kw boiler, which decreases effiecency as a boiler prefers to be on for sustained periods rather than on and off all the time. So balance your needs between hot water demand and central heating efficiency.

Its closer to 82BTUs as well, but ignore that, use kw.

On radiators make sure you understand where the kw rating comes from before buying any.

There specced to delta 50c, which is too high for a condensing boiler.
The rating presumes a flow of 80c, return of 60c. You want delta 40c minimum.

The manufacturer will have the calculation you need to apply but it will roughly be 0.75 so a 2kw radiator is better suited as a 1.5kw radiator when used with a condensing boiler.

Im doing my house at a delta 35 to further ensure the boiler is running at peak efficiency and also to improve warm up times on cold mornings. For 35c its 0.63 so the 2kw becomes 1.2kw.

As you can see you soon need much larger radiators. There is no downside other than space required for going bigger on radiators.

I hope all that makes sense.

What is the delta figure for? I noticed on my boiler there are 2 dials, 1 for the C/H and one for the hot water. I turned the C/H one up thinking it would increase the temp of the radiators and heat the house quicker and therefore use less gas. Or have I got that wrong?
 
What is the delta figure for?

I was confused about this too but I think I've understood it from reading around.

If water goes into a radiator at 80degC and comes out at 60degC then the average temperature of the radiator is 70degC. If the room temperature at that time is 20degC then the deltaT is 50.

In other words, it's the difference between the ambient temperature and the average temperature of the radiator.

I understand that it is possible to balance the radiators to get this deltaT to what you want it to be. Too high a deltaT means that the return water going back to your boiler is too hot which is inefficient.
 
I was confused about this too but I think I've understood it from reading around.

If water goes into a radiator at 80degC and comes out at 60degC then the average temperature of the radiator is 70degC. If the room temperature at that time is 20degC then the deltaT is 50.

In other words, it's the difference between the ambient temperature and the average temperature of the radiator.

I understand that it is possible to balance the radiators to get this deltaT to what you want it to be. Too high a deltaT means that the return water going back to your boiler is too hot which is inefficient.

That's about it. Sorry I'm a bit rubbish at explaining.
 
I'm sure you know considerably more than me, I know next to nothing. I was just intrigued about the deltaT thing when I read what you'd wrote.

How will you measure the temperatures in and out? Simple thermometer?


Infrared spot thermometer would be the easiest, quite cheap on that popular forest site.
 