80 amps protects the cables. Are they only 16mm at the meter position?
It could be that, 25mm tails are required for a 100A supply, 80A fuse will not blow if 80A is exceeded briefly, it takes quite a while for the main fuse to blow, or a substantial short circuit current to blow instantly. In fact an 80A fuse can supply 100A for up to four hours (time chart in below document).80 amps protects the cables. Are they only 16mm at the meter position?
The above document also implies they won't fit 100A fuses anymore, but I've never seen that mentioned anywhere else.
The fuse, or the fuse holder???The fuse that they installed is marked as 100A though so....
Yep, the tails were 16mm, now upgraded to 25mm. Current fuse is 80A. I'm hoping Northern just say it's fine as they won't fit 100A anymore.80 amps protects the cables. Are they only 16mm at the meter position?