Does anyone use or know of a resettable surge protector for their PC. I have used the "cheapie charlie" 4 Gang Surgeguard ones. The problem is once the MOV has blown, if the block is hidden behind a table. You fail to see the green light is extinquished and the block reverts to a plain 4 Gang extension lead and offers no protection.
Learn what that protector was really doing. A potentially destructive surge is hundreds of thousands of joules. How many joules did that power strip claim to absorb? Hundreds? Right off, numbers do not make sense.
Its MOV better not blow. Otherwise a potential house fire existed. The MOV must have a thermal fuse. A surge too large for the protector (but too small to harm appliances) caused a thermal fuse to blow. That surge remain connected to appliances. But MOVs were disconnected, as fast as possible, to avert a house fire. That failure also gets the naive to recommend the protector.
Sometimes a thermal fuse does not blow fast enough. That is the rare and dangerous reason for fire. Be concerned that the protector only claimed to protect from surges that typically do not damage appliances. Start by reading its spec numbers. Be concerned that only a thermal fuse was left to avert fire.
Now, another completely different device does claim protection you want. A completely different device that, unfortunately, has a same name. These connect even direct lightning strikes harmlessly to earth. Must be distant from appliances. Within meters of earth ground. To protect everything inside. If your PSU needs protection, then so does the dishwasher, refrigerator, furnace, RCD, washing machine, air conditioner, and smoke detectors. Only this second type protector protects from a surge that typically damages those.
More important, the effective protector remains functional even after a direct lightning strike. These devices are available from more responsible manufacturers through Keison, Siemens, ABB, and Aelgroup. All names known by any 'guy' for quality.
No protector works by stopping or disconnecting a surge. Did you really think a millimeter gap in a switch or fuse will stop what three kilometers of sky could not? And yet that is exactly what effective protectors are for. So that all surges, including the typically most destructive, do not harm anything. Do not even harm the protector.
Not stop or disconnect a surge. Effective protection connects a surge harmlessly and 'less than 3 meters' to an earthed electrode. The earth ground. A major difference.
Your protector either failed on a tiny surge (be thankful for the thermal fuse). Or was a potential house fire.