Ronski's Solar & battery DIY build with whole house backup

Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Are you designing the railing system/mounting solution yourself, or something you have seen elsewhere? :)

Designed it myself, and will build it myself. Aluminium equal angle 50.8 x 3.2mm, rubber blocks under aluminium pads bolted through the roof, and plenty of polyurethane mastic, although the rubber/ally pads should provide an effective seal, its always good to use some decent mastic just to be sure.
Idea is to keep the height of the panels below that which is required for planning permission.

Panel-Mounts.jpg


Well that was a long hard days work, but my brother and I have successfully installed the two cables, still have some internal tidying up to do, then just a trench to dig and get the cables into the garage. My 43 meters of 25mm SWA actually turned out to be just over 50 when we measured it, so plenty of cable.
 
Associate
Joined
20 Jul 2007
Posts
2,105
Location
A sunnier or damper area than Ron-ski....
This is really interesting Ronski! I've got a similar spare shed which points beautifully South with a 30 degree incline.

I'm watching to see how you get on and may have a go myself if you're successful! Reckon I could get another 8 panels on this roof.

Know the guys will never say it, but we're all rooting for you!! Keep it up!
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Another successful day, tidied up all the cables in the utility room, run in some 10mm T&E for a future induction hob (currently gas hob), tidied up the cables down the wall, and under the oven. Also cemented around the SWA where it goes through the wall.

In the below picture in the foreground is the 25mm SWA in and out, then the kitchen ring main, 6mm T&E for the oven, and the dark grey one is 10mm T&E for the hob. This is all hidden by a 300mm wide pull out unit.

25mm-SWA.jpg


This is the cables running across the back of the utility room, this area is covered with a 3mm steel plate, the gas pipe used to run along there as well, but that was removed a year or so ago, and now enters via the kitchen. Its a pain using cable clips on thermalite, I actually drilled out the cable clips and use 2" nails, then they stay put. Sometimes you can nail them into the mortar joints. The white pipe is the condensate drain from the boiler.

Utility-room.jpg


Tomorrow I just need to put the fridge freezer back in the utility room, and put the baskets back in the pull out unit. Then its a day off. Next weekend I'll start digging the trench to the garage.
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Well that was extremely hard going, rock hard clay soil, numerous stones, the odd house brick and concrete block, also hit the foundations, as they were laid in the wrong place when the extension was built, but at least the trench up to the path is dug.

Tomorrow I just need to dig under the path and the pit the other side of the path by the garage, then drill appropriate holes through the concrete foundation of the garage.

I should have enough SWA left to run a piece back from the garage to the wall top right of the picture, which is the most likely place an ASHP would be installed if we ever got one.

Trench-Day-1.jpg
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
I've got the pit between the path and garage dig quite easily, even the tunnel under the path wasn't too bad to do.

Pit.jpg


Tunnel-Under-Path.jpg


I'm on to the really difficult bit now, drilling 30mm holes through 400mm of concrete, poor old SDS drill is getting rather hot. Got one through, need to drill at least one more, but then I need a hole for the network cable, and also potentially another for the cable for the ASHP. No idea if we'll ever install one but just seems sensible to put the cable in whilst the trench is there.
 

SBo

SBo

Associate
Joined
1 Apr 2022
Posts
267
Location
Bucks
Thank you for sharing all of this and great progress.

Have you checked with the spark that you are getting to sign off the work that they don’t want to inspect it during the job eg routing, cable depth, cable below marking tape at correct depth etc?
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
@Troop it would be a solution, but still with issues, the garage floor slab projects 120mm from the base of the wall, and to get the bend radius on the SWA I would have to cut the concrete out, which is doable and I do have a petrol cutter with diamond blade, so could have done that,

@SBo 6mm wouldn't be enough, given the length, there would be too much voltage drop for solar (even doubling up the cores) I'd much rather play it safe with a nice chunky cable, remember the whole house will be running through it ;)

Two holes are drilled, just need one more at 30mm, and one at 20mm for a network cable.

The additional extra 30mm hole isn't really required, it just makes future installation of an ASHP easier.

The 25mm SWA also easily allows for the required cable derating - 25mm can handle 134 amps, so plenty of scope for derating.
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
I drilled the others holes during the week after work.

Today I got the cables all in, and the pipe for the data cable, unfortunately my warning tape hasn't arrived so can't fill the trench completely.

I used bits of old garden canes as stakes to separate the SWA, which was bedded in sand, then covered in sand, followed by soil, then cut paving slabs (had them spare so why not), then some soil, then should be the tape once it arrives.

I've got a sign to go above the cables where the enter the concrete slab, but this bit between the path and garage will be dug out eventually and filled with decorative stone eventually.


Cables.jpg
cables2.jpg


cables3.jpg
Cables-Covered-slabs3.jpg


My old Stihl cut off saw - bought this with a knackered engine in the mid 90's and rebuilt it, its been very useful over the years.

Slabs.jpg


Trench1.jpg
Cables-Covered-slabs.jpg







Cables-Covered-slabs2.jpg



Starting on the left below is 20mm pipe for network cable, then 25mm SWA for potential future ASHP, 25mm SWA from the grid/meter, lastly 25mm SWA back to the consumer unit.


Garage.jpg


The above cables are not tight against the wall as I will build a stud work frame, with ply, and then cement board for fixing everything to.
 
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
This is coming along nicely, just need the charger now to get the cells and BMS up and running.

This is a good site to track any incoming shipments from CN if you're waiting for stuff to arrive.

 
Back
Top Bottom