- 3 Nov 2004
- UK
My loop is currently running at 1.5GPM. Anything under 1 GPM, I would consider marginally slow tbh. You'll see resistance or temperature vs flow plots start to curve upwards below one GPM, especially impingement blocks.
As a worked example its supposed to help someone do their own calcs and I prefer whole numbers for clarity in the base equation, and I don't use '1' unless its deliberate or I'm not paying attention lol. I also try and keep the derivative values high enough to avoid 0.0x numbers as these always cause problems. The 4GPM value was supposed to be very high to make a point.
I apologise for biting its not like me, I did remove it. Anyway just for you.
Might as well make use of the second example, if you look at the values you can see that as the flow rates increase you see diminishing returns pretty quickly. If you drop below the 1 GPM mark, temp differences across radiators/blocks becomes more significant.
Example.
A computer WC rig with a flow of 0.75GPM & 7/16" bore. The water moves at 0.49m/s. A 250W heat load. Water at 22C has a density of 997 kg/m3 giving a mass flow rate of 0.047 kg/s, specific heat capacity for water is 4186 J/(Kg°C)
250 = 4186 x 0.0474 x dT
Therefore dT = 1.26°C
If you doubled the flow to 1.5GPM? Fluid velocity increases to 0.975m/s, mdot (mass flow rate) increases to 0.094 kg/s.
Therefore dT = 0.63°C
So for the 250w going into the cpu block, say with a coolant inlet temp of 20C, the outlet is 21.26C. If you seriously increased flow by doubling it you only get a marginal improvement of 20.63C