OK mate, won't lie - I can't find it. I could have
sworn I saw on a YouTube channel (along the lines of Heat Geek, so not just some anti-heat pump loon or anything) that they need their arses run off them to keep the flow up at 65ºC, but I can't find the video or mention, nor find much other supporting evidence, so I'll hold my hands up and say that what I said must be incorrect in this case

talking of Heat Geek...
I've just been watching a couple of their vids, and using their cheat sheet/rules of thumb, tried to get an idea of heat loss in our house. We're a 2017 build, and HG reckon that as a rough guide, a post-2006 house will lose anywhere between 20-40W per m^2 of floor space. Having just gone wild with a tape measure, and taking the upper bound of 40W loss, our house
loses just shy of 3kW with an outside temperature of -3ºC. I also measured our radiators, and using HG's radiator output guide, I end up with a total output of 2.9kW while running at 50ºC mean water temperature.
My EPC does also have the U-values for walls, roof, and floor. From what I can see online, if I take the sum of these and multiply it by the temperature differential of outside to inside, I get a rough fabric heat loss. So me this ends up as 15.41W/m2. I assume any ventilation and window losses would need to be added, but it kinda looks like I'd still be at the lower end of the 20-40W guide from HG, so our heat loss of just about 3kW at -3ºC could actually be lower.
So outside air temp of 10ºC now, means the house at 19ºC is losing a minimum of 6W/m2, so rough floor space of 80m2 (ignoring garage conversion right now due to it not being on central heating) means a heat loss of about 480W. The minimum my boiler can put into the heating system is 7kW

meaning my boiler is around 14x too big for the current weather

and around 2.5x too big even for an outside temperature of -3ºC.