Surprised no one has mentioned "diversity" yet?
A ring main is made with two 2.5mm cables. Diversity is calculated in the the regs to de-rate circuits which are unlikely to use their full capacity. Connecting mining rigs is a different scenario and is not suitable for consideration as a ring main. It is moreso a commercial grade installation in a house, and as such the regs do not cater for it.
There is no such thing as a 4.0mm ring main. You would be better off, getting a 64amp breaker in the main consumer unit and sending that via a 10mm FT&E to a 63amp switch fuse running another small distribution unit with two 32 amp MCB's (motor rated to allow for the inrush when they all kick in) and an RCD. Then run 6mm from the 32A MCB's into a double clad twin socket outlet, one for each RCD. Now you can pull what you like without fear of volt-drop, diversity or any other scenario.
The breakers are not there to protect your computers. They are not there to save them in event of an overload. They are there solely to protect the wiring from acting as a fuse and bursting into flames in a short circuit scenario.
Domestic wiring is not designed in the wiring regulations for this purpose; it is designed so that Billy can run a computer in one room, Jackie can do hair for ten minutes with a big hair dryer, Dad can mow the lawn and mum can cook a roast.. but not all together and not continually. If people fail to grasp the risks associated with overloading electrical circuits, then they will witness first hand overloaded and burned out sockets and fires. Sorry to sound like an alarmist but having witnessed such things over the last 30 years, I speak with sentiment and experience.
If you call in an electrician, ensure that you tell him that your equipment will draw X amps from the socket continually. Also tell him that the ambient temperature in that area is X degrees because he will have to derate the cables load carrying capacity due to the excessive ambient temperature. When the ambient rises, the resistance goes up (just like Delta T) and the carrying capacity goes down.
There are some great builds here guys. Just as you've spent a lot of time reseaching your rigs, please do the same with your electrical installations. A domestic sparky even with 17th Edition Part P is not used to seeing an installation like this in a domestic house. Please treat the installation as a commercial one because that is exactly what it is. Sorry for the lecture.