How much money is to be made with this mining buisness? lol
Not more cost!
running 7kw on 1 single 32A ring 24/7 is asking for trouble. If he's telling you its safe then get a new sparky tbh.
Bring another ring down there and split the load as evenly as you can
Well 7000W would the worst case scenario.
7000/240 = under 30A. He should be ok?
How is it worse case? He added up his usage and it came to 7kw.. His miners are on 24/7,..
Yes if you want to calculate a truly worst case then divide by 230 sure.UK is 230/240v mix, 7000/230 - 30.4A
Though the main issue here is also heat, I imagine his seller is HOT (I remember him saying its uncomfortably hot), When the ambient room temp rises, The load a cable can carry drops. IE;
10M length of 2,5MM T&E, Clipped to wall @ 30c ambient = Max 23A
10M length of 2,5MM T&E, Clipped to wall @ 45c ambient = Max 18.1A
Voltage drop calc