Technically no that isn’t how it is supposed to be done.
Electrical accessories should not be fixed to kitchen units.
It should be on the wall, behind the unit, with a hole cut for access.
Also your plastic box has a hole in it and the twin & earth cable that supplies it has no mechanical protection.
Technically the outer sheath can be considered but it’s still ‘rough’
Yes I know most kitchens are like this but it’s incorrect.

Indeed, my sockets for dishwasher and washing machine (also oven) are wall fitted with a blank cover and a spur running to above the worktop and terminating in a singular switch socket to allow simple off/on operation.
 
Soldato
Joined
27 Jul 2009
Posts
5,016
Location
Manchester
Where does it say that in the regulations then?

Have a look at part P of the building regs.
That covers the wiring of domestic properties.

The IEE guide to the building regs state:

wiring accessories (e.g. socket-outlets,switches) should be mounted on the building fabric and not on kitchen furniture.

I would class this as a Cat 3 defect.
Note but not fail the installation.
 
Soldato
Joined
5 Aug 2013
Posts
6,614
Location
Shropshire
Sockets and water don't mix - Maintance lad at work asked me where I had terminated the earth to our equipment as it had blown up- Told him at main incoming earth -Thats ok he said -Turned out someone had put a double socket on floor in bar of cricket club directly below beer tap.
It seemed people were complaining of shocks while having a shower for months.

By the way the sparky put the double socket under my sink as in picture above- would have been better on right side for me..I have put a strip of gaffa tape across the top of socket just in case.
 
Soldato
Joined
27 Jul 2009
Posts
5,016
Location
Manchester
Can you quote it or not? Otherwise stop talking nonsense, sockets are installed in cupboards all the time, in fact it is now the preferred way of doing it.

the iee electritian's guide to the building regulations page 56
5.2.2 Location of accessories in kitchen
wiring accessories (ie socket-outlets, switches) should be mounted on the building fabric and NOT on kitchen furniture.
 
Soldato
Joined
21 Jan 2010
Posts
22,217
Yes, provided that they are securely fixed to rigid parts of the units that are not demountable or otherwise liable to be disturbed in normal service. However, care must be taken to comply with all the relevant requirements of BS 7671, including accessibility for inspection, testing and maintenance, and provision of adequate protection against damage (by impact or water for example) for the accessories, equipment and associated wiring.

Regulation number(s):

  • 530.4.2
 
Soldato
Joined
27 Jul 2009
Posts
5,016
Location
Manchester
Yes, provided that they are securely fixed to rigid parts of the units that are not demountable or otherwise liable to be disturbed in normal service. However, care must be taken to comply with all the relevant requirements of BS 7671, including accessibility for inspection, testing and maintenance, and provision of adequate protection against damage (by impact or water for example) for the accessories, equipment and associated wiring.

Regulation number(s):

  • 530.4.2

Can’t remember the regulation off the top of my head, but check out the one for mounting accessories on wooden patresses.

A clerk of works for social housing wouldn’t allow it.
It’s classed as ‘rough’, although as I’ve said I wouldn’t fail an installation for it providing they are in good condition and not directly under a tap etc.
 
Soldato
Joined
21 Jan 2010
Posts
22,217
Can’t remember the regulation off the top of my head, but check out the one for mounting accessories on wooden patresses.

A clerk of works for social housing wouldn’t allow it.
It’s classed as ‘rough’, although as I’ve said I wouldn’t fail an installation for it providing they are in good condition and not directly under a tap etc.
Well firstly, and it is worrying I am having to tell you this:

The IEE guide to the building regs state:
This book isn't the regs. It is a commercial book interpreting the regs for you. I.e. it has no legal/regulatory basis.

wiring accessories (e.g. socket-outlets,switches) should be mounted on the building fabric and not on kitchen furniture.
This word highlighted.
 
Soldato
Joined
27 Jul 2009
Posts
5,016
Location
Manchester
Well firstly, and it is worrying I am having to tell you this:


This book isn't the regs. It is a commercial book interpreting the regs for you. I.e. it has no legal/regulatory basis.


This word highlighted.

As I said, a clerk of works for social housing installations wouldn’t allow it.
Sockets should be fasted to the building fabric with a local, identified point of isolation.
It’s ROUGH not a fail as I have now said 3x
 
Soldato
Joined
5 Mar 2010
Posts
12,346
I'm not sure how that construes as a "lazy ass cheap skate" when it takes considerably more effort to mount the sockets to the kitchen cabinets than it would to the wall.
 
Soldato
Joined
21 Jan 2010
Posts
22,217
It’s called site experience.
Also where is the accessible point of isolation when the socket is in the back of a cupboard behind 100 beans tins and glass ornaments - which always seems to be the case.
It’s ROUGH
Stick to PAT testing :cry:

Edit: show us your sockets whilst you at it
 
Soldato
Joined
5 Mar 2010
Posts
12,346
Also where is the accessible point of isolation when the socket is in the back of a cupboard behind 100 beans tins and glass ornaments - which always seems to be the case.

How is that any different for a wall mounted socket? Where you have the kitchen cupboard in front of it.
 

Jez

Jez

Caporegime
Joined
18 Oct 2002
Posts
33,073
Only if the clerk of works has read the random book you've read versus the actual regs

I have had similar conversations to this with electricians and building inspectors a few times. I clearly cant tar them all with the same brush but Skodamart seems to fall into this camp.

This is a slight tangent to the specific situation in this thread, but they never seem to understand the difference between the IEEE guide to regulations, and the actual law. Part P is SO small that electrical installations are near enough not governed at all, bar a few select circumstances. I had to literally print the Part P regs out for one building inspector over an electrical installation which i did, and ask him to show me which part of the installation requires notification. He started quoting IEEE to me. He eventually admitted that he'll need to pass the building work over email, after telling me that "he'll need to check this out at his office as he is never usually challenged, he thought that electrical work needed certification" :rolleyes: It was absolutely pathetic.
 