This is the system as it was last night, there is going to be quite a bit changing here.
The DC isolators on the right will be going, these are not required, and in fact considered a fire risk. The combiner boxes at the top have suitable isolation switches for incoming PV, these boxes will also be changed and reconfigured as well.
The 48v to 12v converter next to the inverter will be relocated, as will the 12v fuse box, and the box with the voltmeter in it.
The white fuse box with clear lid will also be going, as its not required, the SCC's (MPPT solar charge controllers) will be wired direct to the Lynx Power In which is fused.
The two external inverter fuses and the DC isolator switch next to them have gone today.
I didn't want to loose solar generation today, so I left the SCC's live, and charging the batteries. This did mean that the Lynx busbars were live with around 50v, and a lot of amps available.
So to lessen the risk of a serious short once the additional Lynx power in was fitted, I removed the positive busbar whilst I modified the negative inverter cables. The Quattro inverter was switched off and isolated from the grid via the change over switches that you can just see bottom left.
This meant the SolarEdge system was powering the house, and any excess from that was exported.
There will eventually be two more solar charge controllers going in, for the two additional arrays.
I also wanted to get rid of the DC isolator, its gets rather hot when passing a lot of current, I've seen 40c on top the case, and 70c+ internally. Its not required, to isolate the inverter I'd switch off the battery and the PV isolators.
The Power In has been modified to take fuses, I also had to cut off and crimp new lugs on the negative cables to get them to sit better.
And with the lid on.
Whilst the inverter was disconnected from the house, I also took the opportunity to update its firmware.