Ronski's Solar & battery DIY build with whole house backup

The battery heating system works, as I'm not currently force discharging the batteries don't get their late afternoon warm up, so they are dropping to 8°c and the heaters turn on and warm them up to 12°c

The first big hump is when the charging kicks in at 2am, then it starts dropping at 5am, where the green and orange lines start rising again is the heating system warming the batteries up. Temperature outside at the moment is 0°c, and the garage is 3°c

Temperatures-heating.jpg
 
They are not bolted to the terminals, they are fitted to the side of the cells, located between the bar which holds the pack together and the cells, the only source of heat there is the cells themselves.

They both measure a few degrees lower than the BMS temperature sensors, so should be plenty of safety margin.

I also calibrated the sensors - beaker full of water and ice cubes, left it to stabilise then set to zero.
 
@reef I'm in total control, so its whatever I want, hopefully I'm not damaging them! I charge them between 2am and 5am at 130A, as there are two batteries that's split in half, so each battery is receiving about 65A, or 0.23C which is battery speak for the charge current related to the Ah capacity of the battery. The manufacture of the cells states "The maximum charge current of the battery does not exceed 1C under 0℃~45℃", I think under should mean between. So I should be perfectly safe charging the cell's as I am. Below freezing they should not be charged, or only with very low currents.


Last night the temperature in the garage got down to 2°c.

PS. There's some interesting info at https://community.victronenergy.com...w-charging-lifepo4-when-freezing-weather.html


.
 
Last edited:
I'm pretty sure I'm doing things correctly, the BMS is set to stop charging at 4℃ and start again at 6℃, battery heating kicks in at 8℃ and stops at 12℃, so hopefully all will be OK. Only issue might be if we get very cold weather, and the heating can't keep up, just means charging will stop, or more to the point won't start, once charging they warm up pretty quickly.
 
My batteries currently down to 12%, so I thought I'd look at home assistant and see how much I'd discharged today, it shows 23.12kWh. This is a calculated figure.

Now if we divide that by 88, then times it by 100, it gives me 26.27kWh, which is not that far off my maximum battery capacity of 29 kWh. Considering I don't use the full cell voltage range, that's pretty good.

Edit. Actually, that's not quite right, there was some discharged between midnight and 2am, then the battery was only charged to 87% by 5am, so usable capacity is greater than above.
 
Last edited:
Before 2am the battery discharged 1.48 kWh.
2am to 5am it charged to 87%
The SOC never increased through out the day.
By 22:51 it reached 10% and stopped discharging - I reserve some in case of a power cut.
Between 5am and 22:51 it discharged 21.99 kWh
I used 77%, so if I divide 21.99 by 77 and times by 100 I get 28.55kWh capacity.


Heatings been on four times this winter, its set to come on when a battery reaches 8c and go off at 12c

Last-30-days-Temps.jpg



Heating relays

Heating.jpg
 
Last edited:
Happy birthday Battery A, its just turned 1 year old :D

Cycle count is 275, so an average of 0.75 a day, not bad considering how hard I push my batteries, although battery B is at 0.83 a day which is probably more representative, as battery A had an easy life to start with. Battery B is 259 days old.

Battery-A-1-Yr-old.jpg
 
Last edited:
Getting very close on my plan for my third solar install :D

I've just popped round to our local City Plumbing, to see if I can get any discount off the web prices, got a little bit off, but minimal really, but every bit helps.

For my NW roof array of 12 panels I've got these short listed.



For the extra £130 I may just go for the 435w panels, they are a newer series, and are a bit better on efficiency and degradation over time.

For the three on the SE wall I'm looking at these, they work out quite expensive per panel including delivery, but I want a physically larger panel (2063mm x 1134mm) as it would look better, would prefer all black, but can't seem to find all black in that size.


This would give an additional 6.795 kWp of solar, and make a total of 15.535 kWp, and should give an estimated 62% more generation.

Figures for the existing system below, are actual figures for the last 12 months, at some point I'll have to see what PVGIS thinks my existing panels should be producing.

Additional-Panels-1.jpg
 
Last edited:
This is the system as it was last night, there is going to be quite a bit changing here.

The DC isolators on the right will be going, these are not required, and in fact considered a fire risk. The combiner boxes at the top have suitable isolation switches for incoming PV, these boxes will also be changed and reconfigured as well.

The 48v to 12v converter next to the inverter will be relocated, as will the 12v fuse box, and the box with the voltmeter in it.

The white fuse box with clear lid will also be going, as its not required, the SCC's (MPPT solar charge controllers) will be wired direct to the Lynx Power In which is fused.

The two external inverter fuses and the DC isolator switch next to them have gone today.

2024-05-24-17-33-46.jpg


I didn't want to loose solar generation today, so I left the SCC's live, and charging the batteries. This did mean that the Lynx busbars were live with around 50v, and a lot of amps available.

So to lessen the risk of a serious short once the additional Lynx power in was fitted, I removed the positive busbar whilst I modified the negative inverter cables. The Quattro inverter was switched off and isolated from the grid via the change over switches that you can just see bottom left.
This meant the SolarEdge system was powering the house, and any excess from that was exported.

There will eventually be two more solar charge controllers going in, for the two additional arrays.
I also wanted to get rid of the DC isolator, its gets rather hot when passing a lot of current, I've seen 40c on top the case, and 70c+ internally. Its not required, to isolate the inverter I'd switch off the battery and the PV isolators.


2024-05-25-11-14-52.jpg


The Power In has been modified to take fuses, I also had to cut off and crimp new lugs on the negative cables to get them to sit better.

2024-05-25-13-59-53.jpg


And with the lid on.

2024-05-25-15-57-15.jpg


Whilst the inverter was disconnected from the house, I also took the opportunity to update its firmware.
 
Not much to update this weekend.

I took this bit of channel.

Channel.jpg


And made six of these, they need another hole drilling in the rear face, but not until I have the panels.
In case you're wondering why I made the brackets instead of using the ones in the kit, it makes fitting the wall brackets simpler, the bottom wall brackets are directly below the upper wall brackets, and not offset.

Channel-Brackets.jpg


Then I took this kit, which I got for £20 each, cheaper than usual.

Mount-Kit.jpg



Which is far too long, whilst they'd make for a nice angle, they would need planning permission, and wouldn't get wife approval!

Kit-too-long.jpg


So modification time.

Modification-Time.jpg


And this is what I end up with, although I need some more bolts.

Lower-Mounts.jpg


These are adjustable from 165 to 225 overall length, the 165mm will give me an angle of 84 degrees, or 200mm from the wall, which is the maximum allowed under permitted development.

Wall-Panel-Mounts.jpg



Now I'd best go and get the grass cut.
 
Last edited:
Went up on the roof again today to install the "Bird Free", hopefully it works as advertised.

I didn't get enough to do both strings, so done all of this one, and some of the other.

There was signs of the seagulls building another nest, but just a few sticks and pieces - I've only seen them up there once since I put my CD rack up, but that's far too noisy in the wind so will have to go.

Incidently, I was looking at the specs for these panels (installed December 2015), they are Solarworld Sunpower 250w panels (I've never washed them), and measure 1675 x 1001, and there efficiency is just 14.91%
Compare that to the ones I've got lined up, 1722 x 1134, 435w and 22.3% efficient, huge improvement.

Bird-Free.jpg
 