Ronski's Solar & battery DIY build with whole house backup

Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Items ordered so far:

  • 16 EVE LF280K - arriving tomorrow apparently
  • JK BMS B2A20S20P-CAN
  • 2.5" touchscreen for BMS
  • Digital YR1035 Lithium Battery Internal Resistance/Impedance Tester
  • EBC-A40L High Current Lithium Power Battery Capacity Tester
Items currently got.

  • 43 meters of 25mm 3 core SWA
  • Wylex 100amp fused switch DSF100M
The last two items on the first list is purely for testing the cells.

I've taken a Victron drawing and modified it to show what I'm aiming to achieve. The bypass switch is just a means to bypass the inverter, if it stops working the whole house loses power, so I need an easy way to bypass it.

Vctron-ESS-Full.png
 
Soldato
Joined
17 Jul 2007
Posts
24,529
Location
Solihull-Florida
Thanks for the info, I may do this for a second set, I suppose the K series hasn't been around long enough to end up with old batteries?


Mine was made feb of this year.
Use a app called LifePoQR Battery QR scanner.

Point your phone at the laser etched markings and it should tell you everything.
If no laser markings. Then they are fake rubbish.
 
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
Mine was made feb of this year.
Use a app called LifePoQR Battery QR scanner.

Point your phone at the laser etched markings and it should tell you everything.
If no laser markings. Then they are fake rubbish.

@deuse What Terminals type did yours come with, the new 2 hole of the older welded post ?.

I'm waiting for another 8 to arrive.
 

SBo

SBo

Associate
Joined
1 Apr 2022
Posts
267
Location
Bucks
How are you going to load manage your home PV vs your garage PV and battery?
The system in your house will presumably see the supply from the garage as if it were the grid, whereas the system in the garage will just see reduced load on the supply side when house PV is producing, but what happens when house PV production is greater than house load? Ideally in that scenario your garage batteries would charge from AC.
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Cells have arrived, couldn't get my phone to scan the code, but once I worked out I needed to enter both numbers together manual entry worked.

Eve LF280K
Date: 2/6/2022
City: Jingmen

There's various other info as well.

No idea if the date is June or February.

Packaging has been updated for the new terminals.
 
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
@Ron-ski there are a couple of the JK BMS (used) on Ebay , same as the one you have on order, seller is taking offers.
might be worth a low offer ;), if you don't fancy waiting for yours to arrive from CN to get up and running.
 
Soldato
Joined
17 Jul 2007
Posts
24,529
Location
Solihull-Florida
Cells have arrived, couldn't get my phone to scan the code, but once I worked out I needed to enter both numbers together manual entry worked.

Eve LF280K
Date: 2/6/2022
City: Jingmen

There's various other info as well.

No idea if the date is June or February.

Packaging has been updated for the new terminals.


That's the 6th of Feb 2022
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
I've checked 7 of the cells in total, and they are all 6th of Feb 2022. I'll check and log all of them tomorrow.

How are you going to load manage your home PV vs your garage PV and battery?
The system in your house will presumably see the supply from the garage as if it were the grid, whereas the system in the garage will just see reduced load on the supply side when house PV is producing, but what happens when house PV production is greater than house load? Ideally in that scenario your garage batteries would charge from AC.

When the house PV production is greater than the house load the Victron inverter will use the excess to charge the batteries, once the batteries are full the excess will be exported.

Another scenario we need to consider is in the event of a grid failure, the suns shining brightly, theres low house load and the batteries being fully charged. The house PV will keep producing power as it still see's grid voltage from the Victron, in this the scenario the Victron inverter can alter the frequency, once it hits 52.5Hz the Soleredge inverter will turn off, well this is what I've been told, so hopefully that's how it will work. Newer Soleredge inverters can actually regulate their output as the frequency rises, whereas the older ones are either on, or off.
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Yes the bottoms of the cells are still covered.

Cell-Bottoms.jpg


All the cells are physically good, there is no damage, only thing I have noticed is the terminals are welded on slightly crooked, some are worse than others though. I don't think this will cause any issues, as there is some leeway in the supplied busbars, but I may well use these flexible busbars - need to check hole spacing.

I've measured the voltage, and every cell is 3.295v, can't carry out any other checks as I don't have the equipment yet.


LF280-K-crooked-terminals.jpg
 
Associate
Joined
21 Aug 2022
Posts
8
Location
Worcs
I'm watching this thread with great interest as it's something I've contemplated doing for a while although in my case it would be a single battery system with or maybe without solar.

The batteries you've chosen look to be a good option.

Are you using 16 batteries, you mentioned 8 were for someone else however I was unsure if you already had another 8?

What is the situation with inverters like the Victron if there is a power cut and you pull more current than they can supply. Do they just trip out?

The other thing I'm interested in is just what is needed from the electricians point of view and if they will be happy signing off something that is homebrew instead of an off the shelf solution.

I look forward to the updates.
 
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
I've ordered 16, someone else in the thread ordered 8 for themselves and 8 for someone else.

One thing to consider if just going for battery storage is payback time, say you have a 14kwh battery, you fully charge it off peak at 7.5p per kWh, that costs you £1.05 to charge it, at the current rate, if you used that 14kwh instead of paying 30p per unit, it would save you £3.15. Probably easier to calculate pay back time though.

If you have a power cut, and draw more power than the inverter can supply it will trip and need resetting, which just means during a power cut you'll have to be careful, only problem I can foresee is unless you set up some kind of warning you wouldn't know there was a power cut.

As for the electrician, mine has said I can do the DC stuff, but he has to do the AC side of it, the tricky part is finding one thats OK doing that, and most don't get involved in solar, and most solar firms want to do a full install, be that just battery or battery and solar, and they want to fit what they want, not what the customer wants. If you're installing just a battery then you only need Part P certification, if you want paying for export currently you need MCS certification, and you only normally get that with a full install.

I've drawn the cell's and busbars, currently they don't seem to make the two that go across the pack - I'll probably need to crimp my own cable for that, or use solid ones. I've uploaded the cell to Sketchup warehouse, just search Eve LF280K.

PS If anybody spots an error in my cells order let me know - I think its correct.

Cell-Pack-with-Busbars.jpg
 
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
Layout is correct, the 2 busbars straddling both rows of cells, might need to be a different length to the ones supplied.(not sure as I have not used that type of terminal)

All looking good.
 
Soldato
Joined
18 Oct 2002
Posts
14,515
Location
West Midlands
if you want paying for export currently you need MCS certification

That is actually not strictly true, you can use 'alternative' certification as MCS isn't a legal requirement, as per the Ofgem rules and SEG licencees are deemed to be able to accept other standards. Check the Ofgem "Guidance_for_seg_licensees_final.pdf" section 4.6, 4.7 and 4.8.

Negotiating with the SEG licensee is easiest done with a G99 system though, as you'll get certification from the DNO which you can argue is acceptable for export if it is acceptable for connecting the equipment to the network, especially as the requirement for a smart meter (for SEG) now means they have a guaranteed correct export figure.

Obviously you need to chose wisely but Octopus have accepted customers without MCS on new systems via their SEG team, and the relevant documentation being provided to show the system is compliant.
 