Had my Octopus survey done today. Not had the full report back yet, but just from word of mouth as the guy was going around:
- Heat loss of house is about 3.9kW (I'd done the fag packet maths at 3.6kW so pretty close). I believe this was the 21ºC indoor/-3ºC outdoor heat loss, but hoping this is confirmed on the report. Certainly means we're down in the 1-2kW heat loss range on "normal" days, and completely proves our 35kW boiler is vastly oversized, as it only modulates down to 7kW!!
- Main heating piping and even the 10mm plastic to the rads would have worked OK
- Need an additional structural survey at about £500 if I wanted the hot water tank in the only cupboard we have (we don't!), which is "floating" above the stairs.
- Loft hatch is too small right now to get a tank up in the loft. Needs professionally doing as the current hatch is the full width between two main beams.
- Additional checks needed but pushed on space even in the loft for where the tank would go vs beams etc. 180L tank looked to be our maximum available if everything aligned.
- Outside location at the back of the house (north facing) very suitable, and close to where the boiler is now.
- Water pressure too low (10L/min vs required 14L/min) - I suspect this is due to nearby housing construction as it's felt a little low over the last couple of months.
Forgot to ask if any rads would have needed changing but according to my own workings, only one or two should have needed attention as we almost always run the house at <50ºC flow temperature on the current gas boiler anyway. Hoping to get a little more from the full report, but realistically it's a no-go, and even the Octopus chap said he'd get the refund started for me.