I have the BMS set to not charge below 3c, hopefully the weather will start warming up soon, and then it will give me time to sort out the heating. I do need to go through all settings, double check them.
I currently have two Victron sensors connected to the Cerbo, they currently read 11 (in the garage) and 12c (outside), the BMS reads 9.7 and 9.8, the weather station says its 5.7c, and my infrared gun says the outside Victron sensor is 3.2c
So I need to find a calibrated temperature gauge, and work what the correct value is, I think the Victron sensors are reading too high and the infrared gun too low.
Just realised I've got a temperature probe on my new UT213C meter, I'll have to leave the probe in the garage and see what that reads later.
I checked the voltages earlier, they all look pretty much spot on, just the MPPT read a little higher than the shunt.
BMS 52.42v
MMPT's 52.51v
Lynx Shunt 52.25v
Meters at battery terminals:
UT213C 52.4v
UT70A 52.2v