Ronski's Solar & battery DIY build with whole house backup

Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
It lives.

Your balance needs to be turned on, set to balance to 0.003V.(think that's the lowest setting it will take)

Just need the electrician and the sun and you're set. :)

Good project for sure.
 
Last edited:
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Your balance needs to be turned on
Balancing was turned on in the settings, but no point balancing at 3.289v, I have balancing set to start at 3.45v which will be what the cells are charged to, so they will balance during absorption.

Here's what I have this morning, hopefully it all looks correct.

BMS-Settings.jpg
 
Last edited:
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
The battery is alive!



Just 0.004v cell deviation, not bad considering I took delivery in August and they haven't been balanced or even been charged.

Battery-A-BMS-App.jpg



Top right on the your pic, it is showing balance turned off in the menu, go to control, make sure the balance toggle is turned on.
When turned on it will always show as on, but only balance to your chosen setting/config (just means the balance function is enabled)

2fT9UY9l.jpg
 
Last edited:
Associate
Joined
25 Oct 2022
Posts
26
Location
UK
Hello Ron, your doing so well and its looking good so far, I bet your pleased fella so far.

I been so busy at home and my project - its just surprising how much time this stuff takes up in your life lol. Mine is up and running and works as expected, you know what I have, it needs tweaking in the multiplus.. the Charger and ESS Assistant - I take it your using the ESS as well mate ?

I know you have the ET112 so I am pretty sure you are going to use ESS, ping me back and will run through my issues I had and how to get around and test before you commission it.. it just saves blurring on here as don't want to over-write your project with my stuff Ron.

Also with the JK and the Victron VE.Config Dynamic Voltage Cut-Offs used within the ESS (if your using ESS..). these will need to be tweaked as the Victrons are safe but will trigger far sooner that JK will. The way I understand it is the JK will control the Cells and not the ESS, I am doing some research now on values and then compiling an email for Victron to advise & review my suggestions via my Distributor (this I have per-arranged already.)

Take care, stay safe mate
 
Last edited:
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
Top right on the your pic, it is showing balance turned off in the menu, go to control, make sure the balance toggle is turned on.
When turned on it will always show as on, but only balance to your chosen setting/config (just means the balance function is enabled)

That is the way it works, it is turned on, but if I change the balance settings so that it will balance then it shows either "Discharging", "Charging" or "Off" depending on what its doing (I can see which cell it is balancing in the list), if the balancing criteria is not met then it will show "Balance: off"

This is the control settings

Balance-On.jpg


@Mafia_GF Yes I will be using ESS, be interesting to hear what issues you had and what you did to resolve, either post here or ping me an email.

Precharge fitted, added a neat little volt meter, voltage dropped as I switched the inverter but had turned on the isolator.


 
Last edited:
Associate
Joined
25 Oct 2022
Posts
26
Location
UK
I am just about to pop out with the good lady, will post here. Have you got the Cerbo connected to the ET112 via RS485 cable yet Ron ?

Also have you reviewed the Charger/Inverter & Dynamic Cutoff Voltages within the ESS yet mate, be interested to what you have yours setup too.
 
Last edited:
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
My 3 work differently, always shows the balance enabled but only starts balancing when it hits my set voltage for balance @3.43v

Must be different firmware as you have the heating option on yours.

How all 3 of mine look/work.

9IjbekBh.jpg
 
Last edited:
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
@Mafia_GF Cerbo is set up, ET112 is connected, just setting up the ESS assistant. Only concern at moment is that it will see the PV production from the SolarEdge system, but it can't see the full picture, as the inverter isn't connected in the mains yet. This is why the VRM (link below) always shows full usage of the solar production at the moment.

@Troop Must just be different firmware, I don't think I specifically bought the heat version, but then the options wasn't straightforward. Not sure if I'll use the heat option or go about it another way. From what I read the BMS doesn't turn the heating on until it reaches the lower cut off temperature, at which point it turns off charging until its heated up tot the recovery temperature. Something I need to look into.
 
Associate
Joined
14 Aug 2006
Posts
1,976
Location
Land of Dragons
@Mafia_GF Cerbo is set up, ET112 is connected, just setting up the ESS assistant. Only concern at moment is that it will see the PV production from the SolarEdge system, but it can't see the full picture, as the inverter isn't connected in the mains yet. This is why the VRM (link below) always shows full usage of the solar production at the moment.

@Troop Must just be different firmware, I don't think I specifically bought the heat version, but then the options wasn't straightforward. Not sure if I'll use the heat option or go about it another way. From what I read the BMS doesn't turn the heating on until it reaches the lower cut off temperature, at which point it turns off charging until its heated up tot the recovery temperature. Something I need to look into.

Just don't let them charge below 0C, being in your Garage you will go below that temp I should imagine.

One important thing to do.....Take a voltage reading from the actual battery output terminals, with a known good and accurate multimeter.
Compare that figure with the reading on the BMS, and change that reading in the BMS to the reading from the actual battery if they are different.
In settings/Calibrate volts.
 
Last edited:
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
I have the BMS set to not charge below 3c, hopefully the weather will start warming up soon, and then it will give me time to sort out the heating. I do need to go through all settings, double check them.

I currently have two Victron sensors connected to the Cerbo, they currently read 11 (in the garage) and 12c (outside), the BMS reads 9.7 and 9.8, the weather station says its 5.7c, and my infrared gun says the outside Victron sensor is 3.2c :confused::confused:

So I need to find a calibrated temperature gauge, and work what the correct value is, I think the Victron sensors are reading too high and the infrared gun too low.

Just realised I've got a temperature probe on my new UT213C meter, I'll have to leave the probe in the garage and see what that reads later.

I checked the voltages earlier, they all look pretty much spot on, just the MPPT read a little higher than the shunt.

BMS 52.42v
MMPT's 52.51v
Lynx Shunt 52.25v

Meters at battery terminals:

UT213C 52.4v
UT70A 52.2v
 
Associate
Joined
25 Oct 2022
Posts
26
Location
UK
@Mafia_GF Cerbo is set up, ET112 is connected, just setting up the ESS assistant. Only concern at moment is that it will see the PV production from the SolarEdge system, but it can't see the full picture, as the inverter isn't connected in the mains yet. This is why the VRM (link below) always shows full usage of the solar production at the moment.

@Troop Must just be different firmware, I don't think I specifically bought the heat version, but then the options wasn't straightforward. Not sure if I'll use the heat option or go about it another way. From what I read the BMS doesn't turn the heating on until it reaches the lower cut off temperature, at which point it turns off charging until its heated up tot the recovery temperature. Something I need to look into.
@Ron-ski
Good man, so your Cerbo can see the ET122, this is good as mine could not, I had a faulty cable and Cerbo :(.. but annoying really but distributor sorted us out pretty quickly. With the setup of your Quatro, don't have anything connected when you set it up, just power it up via AC or DC and the MK3 interface. The Quatro will work out the box just like the Multi.. could not not believe it "Plug & Go.. so speak". I ran some household appliances and was happy as a kid in a sweet shop - by default has a VS setup and will charge from the DNO/GRID automatically.

When you load the ESS Assistant you will see what I am on about, hoping I will get some feedback from Victron but check out the section on Approved Battery's on Victrons website. There are so many questionable settings when using the BMS, I think the way forward is to use what has been setup on the JK, then transpose these into the ESS.. anyway I await what Victron say but have a good idea what they will come back with.


@Troop, yes I fell for the battery Voltage one and not measuing and entring the true pack voltage. Could not understand what was going on untill I just stepped away and re-looked at it, but all good now. Yes Garage does get cold, have a dual temp controller that will monitor and control both shelves, only have one at the moment but based on what I have seen so far I will for sure get another 48V setup mid towards end of the end year.
 
Last edited:
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
There are so many questionable settings when using the BMS, I think the way forward to to use what has been setup on the JK, then transpose these into the ESS.

This is my thinking to, the BMS controls when the battery is shut off etc, so the settings in the rest of the system has to be based on those.

I'm wondering how the cut off settings in the ESS work, presumably it will turn off the DC side, but still pass through the grid if these conditions are met.

I'm putting a spreadsheet of all the settings together, then I can easily look up and see what needs matching up.

PS. Be interesting to hear what Victron come back with.
 
Last edited:
Associate
Joined
25 Oct 2022
Posts
26
Location
UK
This is my thinking to, the BMS controls when the battery is shut off etc, so the settings in the rest of the system has to be based on those.

I'm wondering how the cut off settings in the ESS work, presumably it will turn off the DC side, but still pass through the grid if these conditions are met.

I'm putting a spreadsheet of all the settings together, then I can easily look up and see what needs matching up.

PS. Be interesting to hear what Victron come back with.
Exactly, if you look at the Pylontech they setup these in the ESS (and including Other Battery Brands as well..) basically I read on the Victron Forum as well just to Flat-Curve the Charge curve in the Dynamic Cutoff Voltages and basically let the BMS do the work. I will post below a snapshot from Pylontech.

Wifey was doing the Dinner last night, so had 1 or 2 hob's induction rings on, plus the Microwave and the Kettle. I looked at the VRM portal and I could see it spike up quite high on the load.. what happened was and based on the Cutoff Voltages etc... then the Multi stopped inverting (Battery was about 55% @ about 52/53V.. cannot remember exactly... but with the high load the voltage would drop while supplying the current). At this stage then the DNO/Grid supply was used untill I modified the Cutoff Voltages - so yes it will turn off the DC Only, this is my understanding as well.

What you can do, download VE.Config then go to the VRM Portal.. then to Devices and then you can Download the config off the Quatro/Multi and amend it off-line with VE.Config and then Upload this.. I did this and changed the 0.005C & 0.25C by 1V.. not much.. WELL all kicked back in and I watched the Inverter do it's stuff.. I also saw how much current was been drained from the battery ( I also have a Monitor on the JK BMS as well but mine is the 4" version).. Current discharge started around 20A and then slowly started to rise up to about 85A.. you should have heard the hum from the transformer .. beautiful.... it then all dropped down to about 45A afterwards.. but not long after..

This is why I started to review the settings and really ask the question.. do we really need to have the ESS setup this way as the way I see it.. if your battery pack is managed by the BMS and is roughly/about 53V @ about 50% then with these settings in the ESS and with a sudden load then the inverter will stop inverting ... it won't power down it will just stop inverting as I saw last night.



Snapshot From Victron with ref to Pylontech:
==================================

5.2 Charge Settings​

Charger tab​


Parameter Setting
Battery type Lithium
Charge curve Fixed
Absorption voltage 52.0 V
Float voltage 51.0 V
Absorption time 1 Hr
Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 51.0 V.
Note For off-grid use: ignore the 'bms assistant required' warning.

5.3 Inverter Settings​

In the Inverter tab of VEConfigure

VEConfigure Inverter Parameter Setting
DC input low shut-down44V
DC input low restart48V
DC input low pre-alarm*48V
* The pre-alarm setting is dependant on your preference and on site specific requirements. You may wish for this to be activated earlier in an off grid situation to allow time to start a backup generator.

ESS System Settings​

If you are using the battery as part of a grid connected ESS system, please review the ESS Quickstart guide and Design and Installation Manual.
The settings that are specific to the Pylontech battery in the VEConfigure ESS Assistant are below:
Select the externally managed Lithium battery option
battery_compatibility:ess-battery-system-selection.png


ESS ParameterSettings
Sustain voltage. 48V
Dynamic cut-off valuesset all values to 46V.
Restart offset: 1.2V (Default)
 
Last edited:
Soldato
OP
Joined
3 Dec 2012
Posts
3,641
Location
Kent, much sunnier than Scotland
What you can do, download VE.Config then go to the VRM Portal.. then to Devices and then you can Download the config off the Quatro/Multi and amend it off-line with VE.Config and then Upload this.. I did this and changed the 0.005C & 0.25C by 1V.. not much..

I can connect to the inverter and download the config file, which I can then open in Victron Connect. But not sure how to do this with VE Configure 3, where the ESS assistant is setup - I can do this whilst connected to the inverter directly, but can it be done offline?

What's the 0.005C & 0.25C your refer to?
 
Associate
Joined
25 Oct 2022
Posts
26
Location
UK
Within VRM, you can use "Remote VEConfig" - with this you can Download (.. really uploading the cfg to YOU..), it will save it to your Hard drive somewhere.

Since you already have VEConfig already Ron, just double click this file and it will open with VEConfig, you can them view/amend etc.., save and then upload BACK to the Quatro remotely - clever stuff and well impressive...

For the C values above, these refer to (how I interpret them) as discharge and current drain from the battery with relative to the discharge / cuttoff curve. As you look at each value "Say for example 0.005C & 280AHr Battery", it says if you draw 0.005 x 280 = 1.4A and using the default value of 52.00V and then if the battery drops to 52V or below then you would get an alarm and the DC side would disconnect until the battery voltage would rise above by 1.2V (default value).

This is what happened to me few days back, under heavy current drain and my battery was about 50%.. then with the oven and some other appliances must have been around the 0.25C (or thereabouts..) and the DC side was cutoff untill I made some changes.. it would have recovered by itself but I was keen to see what was happening.

And now with "for example.. Pylontech..", they have flattened this curve and they use their BMS to manage the battery charging curve.

Does this make sense as its quite a minefield really, since I made some small changes its been ok now but I would like to sort them out better etc..
 
Last edited: